ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Photocell
by Docholiday. 01/22/18 10:52 AM
AreMetal Ladders Ever OK For Electrical Work?
by gfretwell. 01/22/18 01:15 AM
VDE 0100 to introduce AFCIs
by sparky. 01/20/18 05:09 PM
MRI LED lights dimmer control replacement - wow!
by Potseal. 01/19/18 08:52 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 20 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
ground size #72994
12/14/06 08:39 PM
12/14/06 08:39 PM
B
bdonus  Offline OP
Junior Member
Joined: Oct 2005
Posts: 5
chicago, il
need to know what size groung conductor to use for the main ground to the water pipe for a 1600 amp service with 4 sets of 600 mcm cables to the utility transformer.

Work Gear for Electricians and the Trades
Re: ground size #72995
12/14/06 09:24 PM
12/14/06 09:24 PM
L
Luketrician  Offline
Member
Joined: Jul 2006
Posts: 272
Sale Creek, TN USA
With the information given, table 250.122 shows 4/0 if the egc is copper, or 350 if it's al/cu. 250.122 (F) talks about conductors in parallel also. This should get you started.


Luke Clarke
Electrical Planner for TVA.

Re: ground size #72996
12/14/06 10:58 PM
12/14/06 10:58 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
You use 250.66, not 250.122
I read it as the max required will be 3/0 copper or 250 MCM al.


Greg Fretwell
Re: ground size #72997
12/14/06 11:23 PM
12/14/06 11:23 PM
L
Luketrician  Offline
Member
Joined: Jul 2006
Posts: 272
Sale Creek, TN USA
Thanks, and apologies for the mix-up, 250.122 is for grounding raceway's and equipment. Seen that first part, where it says minimum size egc, and the rest is history. [Linked Image]


Luke Clarke
Electrical Planner for TVA.

Re: ground size #72998
12/16/06 09:10 PM
12/16/06 09:10 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 840
Michigan
If under the Chicago code its 18-27-250.66 page 93
copper (300) in a 1 1/4 inch conduit or tubing.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,264
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,392 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9655 MB (Peak: 1.1052 MB) Zlib enabled. Server Time: 2018-01-22 16:30:09 UTC