#66471 - 06/05/06 07:01 AM Odd transformer reading  
LearJet9  Offline
Member
Joined: Apr 2005
Posts: 197
Millis, MA USA
While checking a SqD 75KVA 480Pri - 208/120Sec transformer I got some strange readings. (All readings taken several times with more than 1 [TRMS] meter)
A=109.1 B=120.4 C=132.2
AB=208.1 AC=209 BC=208.4
I've not seen this much of a difference on the low side before. Any ideas??

[This message has been edited by LearJet9 (edited 06-05-2006).]


Work Gear for Electricians and the Trades

#66472 - 06/05/06 07:26 AM Re: Odd transformer reading  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Taps in right locations? A could move up, C could move down if taps are available to do so.

Or did this "just" happen on its own? Maybe lost a few windings between A-C.

Is the high side the same way?

[This message has been edited by e57 (edited 06-05-2006).]


Mark Heller
"Well - I oughta....." -Jackie Gleason

#66473 - 06/05/06 08:09 AM Re: Odd transformer reading  
Zog  Offline
Member
Joined: Sep 2005
Posts: 120
Charlotte, NC
Did you do a TTR test? What were the phase current readings? You probally have either unbalanced loads or open/shorted windings.


MV/HV Testing Specialist, "BKRMAN"

#66474 - 06/05/06 08:28 AM Re: Odd transformer reading  
togol  Offline
Member
Joined: Sep 2005
Posts: 421
NW In. USA
gotta good neutral?


Tom

#66475 - 06/05/06 11:10 AM Re: Odd transformer reading  
LearJet9  Offline
Member
Joined: Apr 2005
Posts: 197
Millis, MA USA
Unknown on the neutral at the xmfr but a good neutral in the panel we accessed. No TTR test. High side OK 277/278/277. Don't know when it happened, could have been that way since the original installation 4 years ago. We were there to T.S. a problem with the sign and found these readings downstream from the xmfr. We did not have access to the xfmr itself. I just thought that was odd to get a good 208 but not on each phase. So, the taps effect the individual phase but not the 208??

Added note: We had access to view the xmfr, but not to open or work on it.

[This message has been edited by LearJet9 (edited 06-05-2006).]


#66476 - 06/05/06 12:35 PM Re: Odd transformer reading  
Radar  Offline
Member
Joined: Apr 2004
Posts: 349
Los Angeles, CA
Not so odd - I've seen similar readings (actually larger variations) on a buncha new transformers just installed where the installer did not realize he needed to bond the neutrals and the grounds. He assumed they just came that way, ready to go. Phase to phase readings look OK, phase to ground readings vary according to relative load imballance on the particular transformer. In our case, we had installed 10 of these things, all were unbonded. We got some really wierd readings.

You need to have a look into that transformer, check out the N-G bonding.

Radar


There are 10 types of people. Those who know binary, and those who don't.

#66477 - 06/05/06 07:39 PM Re: Odd transformer reading  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Quote
Unbalanced secondary voltages:
Overload; tap connections not on identical tap positions; neutral ungrounded

Re: Page 26 of Squar D manual


Mark Heller
"Well - I oughta....." -Jackie Gleason

#66478 - 06/05/06 08:08 PM Re: Odd transformer reading  
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 305
Maryland USA
I had a transformer giving me goofy readings - It turned out to be XO was not bonded . Tightened the XO Bond and everything straightened right up.
If I was questioning the voltage readings I would test them at the transformer if possible.


#66479 - 06/06/06 05:45 AM Re: Odd transformer reading  
LearJet9  Offline
Member
Joined: Apr 2005
Posts: 197
Millis, MA USA
We told the customer they should have the terminations checked at the xmfr. However, their general philosophy of; "If it isn't affecting business, who cares." Will win out I'm sure.


#66480 - 06/06/06 06:52 AM Re: Odd transformer reading  
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 854
Titirangi, Akld, New Zealand
Hi, you need to get access to the transformer itself.

1. Check neutral, earth connections from the TF.
2. Also do a current and voltage check on each phase and check for overload at the TF.
3. Check if tappings are set correctly and not one tap has been plugged or connected differently than an other tap.
4. Check if there are any signs of overheating, discoloured windings, smell of hot varnish.
5. Check temperature of TF, it will certainly tell you if it's overloaded.
6. Do an insulation check on TF if they allowe you to shut it down. All wires disconnected. ( make a note of where the wires go before you take them off )

BTW is this a dry TF or oil filled TF?

If oil, check oil level.

edited for typo's RF.

[This message has been edited by RODALCO (edited 06-06-2006).]


The product of rotation, excitation and flux produces electricty.

Page 1 of 2 1 2

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.026s Queries: 15 (0.005s) Memory: 0.8180 MB (Peak: 0.9940 MB) Zlib enabled. Server Time: 2017-07-28 17:00:06 UTC