Tripping breaker #53362
06/22/05 03:04 PM
06/22/05 03:04 PM
L
leespark  Offline OP
Member
Joined: Jan 2004
Posts: 54
Massachusetts
Last week we installed some low voltage linear lighting in some display cases in a library. We removed some old fluorescent strips which were existing and used the original circuit and 2 switches that controlled the lights.

The new lights, which were supplied by the building manager, is a 24 volt system. It now consists of 2 600 watt transformers with built in circuit breakers feeding approx. 10' of lighting per transformer.

Everything fired up fine, then I get a call the lights are out. It turns out the breaker has tripped. I check the load on the circuit and each transformer is drawing about 3.5 amps, total circuit 7 amps. So I decide to change the older SqD QO bolt on breaker.

After changing the breaker I'm discovering that the circuit still trips especially when I rapidly turn the switches on and off and not 1 particular switch. Either switch being turned on and off rapidly will cause this to trip.

I need to return tomorrow morning before the library opens to dig a little deeper. I'm wondering if a problem on the neutral might be the problem however there does not seem to be a logical explanation. The wiring is BX in very good shape (the building is about 30 years old).

Any suggestions would be appreciated.

Thanks

Work Gear for Electricians and the Trades
Re: Tripping breaker #53363
06/22/05 04:20 PM
06/22/05 04:20 PM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
Lee
You need to provide more info.
1 Are the transformers 120/24 volts? Are they on the same circuit?
2 "It now consists of 2 600 watt transformers with built in circuit breakers feeding approx. 10' of lighting per transformer" Is this the breaker that tripped or the line circuit breaker?
3 What size is the circuit breaker?
4 Is the amperage measured on the 120 volt side?

These types of transformer can draw large inrush currents. Sometimes 40 x FLA. If you have a good voltmeter you can measure the max current and see.

Re: Tripping breaker #53364
06/22/05 04:35 PM
06/22/05 04:35 PM
L
leespark  Offline OP
Member
Joined: Jan 2004
Posts: 54
Massachusetts
Bob, thanks for responding.

The transformers are 120v primary, 24v secondary.

Yes, they are on the same 120 volt circuit.

The 20 amp SqD bolt single pole breaker is tripping.

The "breakers" on the individual transformers have not tripped.

I measured the amperage on the primary side at the circuit breaker using a clamp on amp probe.

Re: Tripping breaker #53365
06/22/05 04:38 PM
06/22/05 04:38 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I think inrush current may be the problem. Square D makes some breakers called "high inrush." I've had to use these on some multiple ballast signs that tripped the breaker(s) for no detectable reason.

The stock # is QOB120HM

Good luck

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: Tripping breaker #53366
06/22/05 07:53 PM
06/22/05 07:53 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
I'm with Bob and Tom here.... You probhably notice a "ping", or "pong" when you flip the switch? How many watts are you running on each transformer?

Are you using a decent "lighting" Transformer, or one of those buck and boost T's with a few modifcations of adding CB's from a "Manufacturer". Some of the cheaper ones will just modify a buck and boost. That will give them a very high in-rush. (As they were designed for power, not lighting...) You can try the breaker suggested, or if possible use a dimmer to ramp up the switching current, or switch seperate.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Tripping breaker #53367
06/22/05 08:16 PM
06/22/05 08:16 PM
L
leespark  Offline OP
Member
Joined: Jan 2004
Posts: 54
Massachusetts
I think you guys are right on the money with this. I'm going to try to locate that breaker tomorrow and give it a shot.

The transformer is made by the same manufacturer as the linear lighting. It is a similar system to Juno Trac 12 but the name escapes me right now.

I'll post back and let you all know how it works out.

Thanks a lot for the info!

Re: Tripping breaker #53368
06/22/05 08:36 PM
06/22/05 08:36 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Juno LV tansformers are buck and boost's with black paint, and a CB added...


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Tripping breaker #53369
06/22/05 08:52 PM
06/22/05 08:52 PM
P
poorboy  Offline
Member
Joined: Jun 2005
Posts: 124
Central Maine
This is good stuff, you guys amaze me with the amount of suggestions that so much collective experience makes possible. Really glad to have found this site!

Re: Tripping breaker #53370
06/22/05 09:44 PM
06/22/05 09:44 PM
S
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
Wouldn't installing one of those Maestro touch dimmers where the lights turn on and off gradually (theatre dimming) make a difference?

***Edit***

Oops...just reread the thread, I see E57 already suggested the dimmer thing. Sorry.

[This message has been edited by Sandro (edited 06-22-2005).]

Re: Tripping breaker #53371
06/22/05 10:07 PM
06/22/05 10:07 PM
J
Jps1006  Offline
Member
Joined: Jan 2004
Posts: 615
Northern IL
I have had Meastro's fail because of a little plastic piece behind the plate. I would leary of using it in a commercial environment unless it was to be used by a soft, gentle librarian.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,547 Are you busy
180,357 Re: Forum
170,836 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.035s Queries: 15 (0.005s) Memory: 1.0233 MB (Peak: 1.1982 MB) Zlib enabled. Server Time: 2018-01-19 13:37:02 UTC