Fixture whips #50083
03/23/05 05:49 PM
03/23/05 05:49 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
I looked at a job that had all of the chain hung flourescent fixtures fed with SJO type whips.The area is a dry location,a warehouse.The owner wants more lights put up. My question is about the SJO cord feeding the fixtures.Usually I use MC w/ stranded conductors to feed chain hung fixtures.I'm looking at 410.67(c).I would think the SJO cord is a violation. Any feed back is greatly appreciated. ToHo

Work Gear for Electricians and the Trades
Re: Fixture whips #50084
03/23/05 06:52 PM
03/23/05 06:52 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
ToHo,

You're weeding in the wrong pea patch. 410.67(c) deals with "Special Provisions for Flush and Recessed Luminaires."

Put your hoe in the row marked 410.30(C)(1). The existing installation may still be incorrect, but at least you'll be citing the correct section.

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: Fixture whips #50085
03/23/05 07:23 PM
03/23/05 07:23 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
Tom.. Thanks
I skipped right by 410.30
The only question I have would be the type of connector you would use for the SJO. The strain relief connectors w/ the grips go for $15.00 each.Anyone have any cheaper connector that is listed for this use.Thanks ToHo

Re: Fixture whips #50086
03/23/05 07:35 PM
03/23/05 07:35 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Fixture whips #50087
03/23/05 08:24 PM
03/23/05 08:24 PM
F
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
I'd check with inspection.We were allowed to run SJOW whips to switched receptacles on the premise that the lights may have to be removed if we have need to move large equipment around the plant.The receptacles had to be placed directly above the light.The SJO does begin to rot in hot ceiling space after 5 or so years.

Re: Fixture whips #50088
03/23/05 09:01 PM
03/23/05 09:01 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Most two-screw romex connectors are listed for use in this sort of application with SO cord- check the box. They cost maybe 30 cents a piece.

Re: Fixture whips #50089
03/23/05 09:02 PM
03/23/05 09:02 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
Thanks for the replies.
I'm wondering if the existing installation w/ SJO cord was installed because of the distance between the fixture and the junction boxes.Using a MC whip would limit you to 6ft.I can't find any limitations in lenth w/ flexible cord in 410.30(c)(1)??Thanks ToHo

Re: Fixture whips #50090
03/23/05 09:30 PM
03/23/05 09:30 PM
S
safetygem  Offline
Member
Joined: Jan 2002
Posts: 119
Ohio, USA
Toho... no limit on length for the cord, but, remember the requirements in 410.22. I've seen people get pretty sloppy with this type of installation.

Quote
410.22 Luminaire (Fixture) Wiring — General.
Wiring on or within fixtures shall be neatly arranged and shall not be exposed to physical damage. Excess wiring shall be avoided. Conductors shall be arranged so that they are not subjected to temperatures above those for which they are rated.

Re: Fixture whips #50091
03/24/05 07:35 PM
03/24/05 07:35 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
ToHo- Why would there be a limit on the length of an MC whip. It can be longer than 6' as long as its supported. Cable tie it to the chain that's supporting the fixture and you're good. SJO cord can only be used if it plugs in to a receptacle at the ceiling. You cant hard wire it to a j-box because that makes it a permanent wiring method.

Re: Fixture whips #50092
03/24/05 10:18 PM
03/24/05 10:18 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
Thanks Greg..
Through my entire career w/ Local 3 I never made a fixture whip longer than 6ft.That was drilled into our heads from day one. Now that I'm on my own & looking for some basis on the rule, I only see 6ft. max rule in 410.67 Special provisions for flush and recessed Luminares ..Also.. It seems the use of stranded conductors in the whip is mentioned in 410.28 for chain hung fixtures etc. I can't honestly say I have ever fed any drop in flourescent fixtures with solid wire. You learn something new everyday. I thank everyone for their responses...keep them coming!! Thanks again ToHo

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.032s Queries: 15 (0.009s) Memory: 1.0227 MB (Peak: 1.1993 MB) Zlib enabled. Server Time: 2018-01-18 21:52:07 UTC