#48314 - 02/09/05 11:18 AM Confused about transformers  
swampy  Offline
Junior Member
Joined: Feb 2005
Posts: 1
Bancroft, WI U.S.
I 'm studying for my Journeyman's. One question is ; A 10 kva trans. is 240/120v. step down. secondary ocp is 125%. What is max. cb required for primary if eff. is 100%?

Can anyone give me some pointers? Thank you!


Work Gear for Electricians and the Trades

#48315 - 02/09/05 12:20 PM Re: Confused about transformers  
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
The formula for pri current is kVA/E pri times the phase multiplier. In this case a single-phase multiplier is 1. If it were 3 phase the multiplier would be 1.73.

It would be a good idea to read section 450.3(B) and study the table. You should understand that in general a transformer operating at 600V or less is considered (in general) when the pri OCPD is set at 125% of the pri FLC) The table will go on to indicate that in cases where there is OCP at the secondary of the transformer which is set at 125% of the secondary FLC, the pri OCPD may be increased to 250% of pri FLC.

Your transformer should have a 41A pri and 2.5 X 41 yield 102. (see notes to tables ) I'd call it 100A.


#48316 - 02/10/05 12:33 AM Re: Confused about transformers  
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
Cpal said "Your transformer should have a 41A pri and 2.5 X 41 yield 102. (see notes to tables ) I'd call it 100A."
That is correct. Note that the table allows you to go up to 250% but not exceed that figure. If the 250% does not yeild a standard
fuse or breaker, you may not round up.



Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 222
Joined: February 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.003s) Memory: 0.7512 MB (Peak: 0.8750 MB) Zlib enabled. Server Time: 2017-05-26 11:14:12 UTC