200 amp OH Service #47072
01/07/05 11:22 PM
01/07/05 11:22 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
Customer has 200amp OH service w/ 2 100amp meters(double gang meter) feeding 2 100amp panels w/100amp main breakers.Customer wants one panel to be up graded to a 200amp.So the end result would be a 200amp & 100amp panel. I would think I would have to upgrade to a 2 gang 200amp meter box.The house has gas heat and appliances. The load calculation on the house isnt changing by a large amount. Just needs more breaker space for attic renovation.That said ... the 200amp OH service should be ok.. any input is greatly appreciated..ToHo

Work Gear for Electricians and the Trades
Re: 200 amp OH Service #47073
01/07/05 11:40 PM
01/07/05 11:40 PM
N
Norstarr  Offline
Member
Joined: Sep 2004
Posts: 86
Wi
You would have to upgrade to the two 200 amp meter sockets. Sounds like a lot of work if the loads aren't changing. How about installing a 30 circuit 100 amp main breaker panel and upgrading the grounding? SQD makes one and I believe Cutler Hammer does to.
Ron

Re: 200 amp OH Service #47074
01/07/05 11:48 PM
01/07/05 11:48 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
customer wants the 200amp panel for future use if necessary. I don't believe The utility Co. rates the residential service as a continuous load?(only commercial) I'm not sure at what point the utility Co. would want me to upgrade the 200amp OH service. ToHo

Re: 200 amp OH Service #47075
01/08/05 02:05 PM
01/08/05 02:05 PM
W
Wirenuttt  Offline
Member
Joined: Nov 2002
Posts: 267
Massachusetts
You may want to consider the Milbank number
U2601-XL. It's a 2-gang horozontal one 100 amp and one 200 amp. Now you can have a 200 amp main 40 ckt on one side and a 100 amp 30 ckt on the other. They're mostly used where there's one larger sq ft home next to a smaller apt/in law.

Re: 200 amp OH Service #47076
01/08/05 09:38 PM
01/08/05 09:38 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
wirenutt..
thanks..I did not know milbank made a combo meter enclosure like that.. I just have to check with the poco to see if 4/0 seu service riser will be large enough for both services.. Thanks again ToHo

Re: 200 amp OH Service #47077
01/09/05 12:14 AM
01/09/05 12:14 AM
N
Norstarr  Offline
Member
Joined: Sep 2004
Posts: 86
Wi
Hey Wirenutt,
35 years in the business and thats the first time I've heard Milbank had such a meter socket. Very interesting. Will have to see if WE energies approval is on that one for future use. Education never comes to an end.
Ron

Re: 200 amp OH Service #47078
01/10/05 08:40 PM
01/10/05 08:40 PM
W
Wirenuttt  Offline
Member
Joined: Nov 2002
Posts: 267
Massachusetts
I didn't know it was made til I had started working in a supply house. After years in the field now have acsess to all this info., figures, LOL....


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,548 Are you busy
180,358 Re: Forum
170,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.003s) Memory: 0.9817 MB (Peak: 1.1325 MB) Zlib enabled. Server Time: 2018-01-19 17:40:46 UTC