Why not 2 grounding screws on receptacles? #43439
10/14/04 07:56 AM
10/14/04 07:56 AM
C
chimo  Offline OP
Member
Joined: Oct 2004
Posts: 16
All-

If you are wiring a series of outlets, and are allowed to use one set of screws for the line, and one set for the load, why do you have to pigtail the ground? I understand the ground screw is only rated for 1 conductor, so why don’t they make outlets with 2 ground screws? Wouldn’t this make for a safer connection (eliminating a possible weak connection with a wire nut?)

Thanks,

Chimo

Work Gear for Electricians and the Trades
Re: Why not 2 grounding screws on receptacles? #43440
10/14/04 09:47 AM
10/14/04 09:47 AM
C
Creighton  Offline
Member
Joined: Jan 2002
Posts: 59
Hayward, CA
See 250.148. The continuity of the grounding conductors shall not be interrupted. First ground the box, then ground the receptacle to the box, so that removal of the receptacle willlnot interupt the grounding circuit.
Creighton.

Re: Why not 2 grounding screws on receptacles? #43441
10/14/04 12:52 PM
10/14/04 12:52 PM
A
Anonymous
Unregistered

If you are talking about a duplex receptacle you might think about it this way. Your wiring two individual receptacles and have the option to break the tabs to either half switch or wire with two different hots. Or, to break off both tabs and wire with two individual circuits / neutrals. either way your only grounding one strap or yoke.

Re: Why not 2 grounding screws on receptacles? #43442
10/14/04 01:07 PM
10/14/04 01:07 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Grounding is so important that it cannot depend upon the device for it's continuity. Like Creighton said, first the continuity of the ground is assured, then you bond the receptacle to the grounding system via pigtails or jumpers. By the way, a wire nut is a superior connection, in my opinion. Although either, done correctly, is an excellent connection.


Earl
Re: Why not 2 grounding screws on receptacles? #43443
10/14/04 01:38 PM
10/14/04 01:38 PM
C
chimo  Offline OP
Member
Joined: Oct 2004
Posts: 16
Now I understand, continuity is the key. Which brings up one more question- In a duplex config., why only allow 1 conductor under the ground? If the grounds were twisted together, you would maintain continuity if the outlet was removed. Is it just a matter of solid contact between the wires & screw?

Re: Why not 2 grounding screws on receptacles? #43444
10/14/04 05:15 PM
10/14/04 05:15 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
The basic rule is one wire per terminal, so that limits you to one wire under the screw. This rule applies to all terminals, not just equipment grounds.

Twisting the wires together is not recognized as a splicing method, you have to finish the job with a splicing device (such as a wire nut) or brazing, welding or soldering.


Few things are harder to put up with than the annoyance of a good example.
Re: Why not 2 grounding screws on receptacles? #43445
10/14/04 05:32 PM
10/14/04 05:32 PM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
We pigtail all conductors, I thought that everyone did. It is not considered code compliant to run the full ckt. current through a device strap.

I don't know the code reference off the top of my head but that's the enterpretation here in Nebraska.

GJ

Re: Why not 2 grounding screws on receptacles? #43446
10/14/04 06:04 PM
10/14/04 06:04 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
GJ,
Quote
It is not considered code compliant to run the full ckt. current through a device strap.

That will be news to UL as the listing says that you are permitted to use the device to splice the circuit conductors.
Don


Don(resqcapt19)
Re: Why not 2 grounding screws on receptacles? #43447
10/14/04 07:04 PM
10/14/04 07:04 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
I too splice all conductors, UL listed or not. Personnal quality / prefferance. (Not saying that those who do use the device terminals perform lesser quality work.) But I would have a kiniption if one of my guys does it, as I feel it sooner or later may become a call back for warrantee. And, I would defininatley hit the roof if it were done on a 3, or 4 wire circuit. This could subject the circuit to under/over voltage should the neutral fail. And, that may also be a code requirement for the 'grounded conductor', as well as the 'grounding conductor'. (I'm on my other computer and can't check now.)


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Why not 2 grounding screws on receptacles? #43448
10/14/04 08:31 PM
10/14/04 08:31 PM
E
electricman2  Offline
Member
Joined: Nov 2003
Posts: 269
Thomasville, NC USA
Pigtail is required for the grounded conductor if part of a multiwire circuit.


John
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
Potseal 15
sparky 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,862 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.051s Queries: 15 (0.020s) Memory: 1.0227 MB (Peak: 1.2004 MB) Zlib enabled. Server Time: 2018-01-22 18:21:18 UTC