Water pipe ground/ground rods #41388
08/25/04 04:38 PM
08/25/04 04:38 PM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
In an overhead service drop for a residential service, where does the source transformer get its ground besides the actual center tap on the windings. The water pipe is in the ground and there has to be that connection through the actual dirt ground.


The Golden Rule - "The man with the gold makes the rule"
Work Gear for Electricians and the Trades
Re: Water pipe ground/ground rods #41389
08/25/04 04:46 PM
08/25/04 04:46 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The utility will drive a ground rod at the pole that supports the transformer, as well as additional ground rods at every third pole or so. Different utilities will have different rules based on local ground conditions and the likelihood of lightning strikes.


Earl
Re: Water pipe ground/ground rods #41390
08/25/04 04:47 PM
08/25/04 04:47 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I am not sure what you mean when you say.

Quote
The water pipe is in the ground and there has to be that connection through the actual dirt ground


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Water pipe ground/ground rods #41391
08/25/04 05:37 PM
08/25/04 05:37 PM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
iwire, I mean the water pipe runs through the ground and has to be an extra path back to the Utility ground.
Along with the ground rods.


The Golden Rule - "The man with the gold makes the rule"
Re: Water pipe ground/ground rods #41392
08/25/04 05:57 PM
08/25/04 05:57 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Not exactly, the grounding electrodes installed at a service will not help clear a fault at 120 volts.

They may help with lighting and a power company fault that sends high voltage onto the neutral.

Quote
250.4(A)(5)Effective Ground-Fault Current Path. Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a permanent, low-impedance circuit capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. The earth shall not be used as the sole equipment grounding conductor or effective ground-fault current path.


The neutral conductor through the bonding jumper is the Effective Ground-Fault Current Path back to the source for 120 volt ground faults.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Water pipe ground/ground rods #41393
08/25/04 06:36 PM
08/25/04 06:36 PM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
Actually the utility ground is the total of all the service ground rods and water service grounds tied together by the secondary neutral on the street. Everybody contributes.

-Hal

Re: Water pipe ground/ground rods #41394
08/25/04 07:04 PM
08/25/04 07:04 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Hal I agree they do all contribute but at 120 volts not to much.

The Code uses 25 ohms as a reference for a minimum for one rod or you need to toss in another one.

Lets say all the electrodes together get you down to 8 ohms of resistance.

At that level of resistance a fault (not including the neutral) will draw 15 amps.

This will take a long while to trip a 15 amp breaker if ever. [Linked Image]

The electrodes contribution will be a very small percentage of the total fault current once you include the neutral.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Water pipe ground/ground rods #41395
08/26/04 09:26 AM
08/26/04 09:26 AM
R
rowdyrudy  Offline
Member
Joined: Nov 2002
Posts: 169
Mascoutah, IL USA
The vast majority of UG water lines installed within the past 30-40 years are PVC. Not much of a ground, but a friend was red-tagged because he didn't bond to the water line )PVC).
Rowdy

Re: Water pipe ground/ground rods #41396
08/26/04 07:57 PM
08/26/04 07:57 PM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
Bob I agree also. I think aldav53 is a bit unclear as to the purpose of grounding hence the confusing question.

The "ground" is not current carrying. The unbalanced and fault current is carried by the neutral conductor that connects to the transformer center taps and runs from pole to pole and into every service.

This neutral is grounded at each service (through ground rods and bonding to the water line) as well as at each transformer with a ground rod. The purpose of grounding is to offer some protection from lightning and primary power crosses as Bob points out.

If the area has a continuous metallic water system, yes the pipe is, in effect, in parallel with the neutral on the poles and also in contact with the earth providing a ground.

-Hal

Re: Water pipe ground/ground rods #41397
08/26/04 09:58 PM
08/26/04 09:58 PM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Hal, I'm just wondering where the transformer ground is that is linked (has a path to) to the connection to the water pipes and ground rods at the home.


The Golden Rule - "The man with the gold makes the rule"
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 15
Popular Topics(Views)
243,566 Are you busy
180,366 Re: Forum
170,844 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.044s Queries: 15 (0.022s) Memory: 1.0234 MB (Peak: 1.1981 MB) Zlib enabled. Server Time: 2018-01-20 21:06:09 UTC