Sleeve for NM cable #32679
12/31/03 09:52 AM
12/31/03 09:52 AM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Happy new year to all!
When using conduit as "protection from physical damage" for nonmetallic-sheathed cable as permitted in section 334.15(B) what is the maximum length of conduit that can be used as a sleeve.
Since the Code is not specific I suppose it might vary according to AHJ.

Frank

Work Gear for Electricians and the Trades
Re: Sleeve for NM cable #32680
12/31/03 10:31 AM
12/31/03 10:31 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Hello Frank. Happy New Year to you.
This has been discussed in one way or another(see 250.86, exception 2) in several different forums.
There seems to be no consensus as to what constitutes a "short section".

BTW,
I say anything less than a full length.

Re: Sleeve for NM cable #32681
12/31/03 11:21 AM
12/31/03 11:21 AM
G
George  Offline
Member
Joined: Feb 2002
Posts: 375
You can use as much as you want to.

For less than 2' you can ignore the fill and derating requirements.

Re: Sleeve for NM cable #32682
12/31/03 12:04 PM
12/31/03 12:04 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,888
NY, USA
Frank,

Happy New Year!

I've been told any length was OK as long as one end was open. On a closed conduit system I don't know.

Bill

Re: Sleeve for NM cable #32683
12/31/03 05:42 PM
12/31/03 05:42 PM
E
Electric Eagle  Offline
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
As long as the conduit is sized properly for the size and number of conductors inside the NM, there isn't a restriction on NM in conduit. Most NM is THHN/THWN-2.

Re: Sleeve for NM cable #32684
01/07/04 11:48 AM
01/07/04 11:48 AM
R
rizer  Offline
Member
Joined: Jan 2004
Posts: 91
bradenton ,fl.,usa
how are you using the sleeve? for what pupose, does the sleeve terminate into a box etc????


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,522 Are you busy
180,321 Re: Forum
170,812 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9739 MB (Peak: 1.1196 MB) Zlib enabled. Server Time: 2018-01-17 14:58:00 UTC