First final inspection. #23425
03/17/03 09:18 PM
03/17/03 09:18 PM
M
master66  Offline OP
Member
Joined: Apr 2002
Posts: 257
Masontown, PA, USA
I am going to be doing my first final inspection on a new single family dwelling in a few days and was wondering if anyone on here uses any type of check list when performing inspections.

If so, what kind and where could I get one?

Work Gear for Electricians and the Trades
Re: First final inspection. #23426
03/18/03 06:11 AM
03/18/03 06:11 AM
G
gramps  Offline
Member
Joined: Aug 2002
Posts: 112
ohio
my first final was sort of "anti-climactic". only took about 5 minutes.
after getting "gigged" for a couple of items, on my "rough-in", when i got ready for the final, i was stressed out beyond belief. i called to make the appointment with the inspector, and waited all day for him to show up.. all the while, double-checking, triple checking, etc., while driving my crew nuts. the inspector showed up about 3:30 p.m., looked at my drawings, walked around a bit, asked me a couple of questions about my grounding system, signed off, and left....about 5 to 10 minutes at the most. as he was driving away, i thought, "is that it? thats all there is?" lol.. i only wish that some of my others had gone so quickly and smoothly... [Linked Image]


[Linked Image]
gramps

Re: First final inspection. #23427
03/18/03 06:50 AM
03/18/03 06:50 AM
T
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
(I'm not an electrician.)

Take a look here: http://www.codecheck.com/

Re: First final inspection. #23428
03/18/03 06:08 PM
03/18/03 06:08 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Master66:
With my AHJ hat "on":
Basically, this is a resi final:
Switches/lights all work, all fixtures installed.
Receptacles are all "hot"; polarity & grounding are OK
All plates are on; no gaps etc.
Mechanical equip wired correctly
Correct fuses/cb's for HVAC units
Required GFI, etc in unfinished basement area
Panel marked correctly
Ck serviceif not done on other inspection
Ck smoke/co2 detectors.
Ck exterior lighting and GFI's.
(All GFI devices are tested)

That should be it.

A "good rapore" with your AHJ's should be established, if you can.

PS: How was the "rough"??
Good Luck!
John


John
Re: First final inspection. #23429
03/18/03 06:37 PM
03/18/03 06:37 PM
M
master66  Offline OP
Member
Joined: Apr 2002
Posts: 257
Masontown, PA, USA
Thinkgood,

Thanks for the link. That will work well as a memory jogger.

I probably should clarify something. I AM an inspector getting ready to do my first final inspection.

Re: First final inspection. #23430
03/18/03 07:54 PM
03/18/03 07:54 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Master66,

As John said, when I do my final res. inspection, I check about80-90% of the receptacles in the house to make sure of proper polarity. You look for either a light or switched on recp. in all rooms. I check ALL GFCI's, Not every light has to be there. ( i.e. sconce lights or fancy chandilers on back order.) as long as there is a temp. light. Check for HVAC in attic (with lights and recpt.) Check the service for proper markings, HVAC outside for correct OC protection. As for a good reference guide check out Joe Tedesco's "BASIC CHECK LIST FOR BUILDING ELECTRICAL INSPECTORS." It is a very good book. I was also making out a list of the top ten violations for roughs and finals.

Re: First final inspection. #23431
03/18/03 08:24 PM
03/18/03 08:24 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Master66:
A new AHJ, I apologize....
I thought you went out on your own, and had your first "final".
Sorry......
I have an NFPA "Inspection List" (checklist) at the AHJ office. I'll get a source and post it Thurs/Fri if ya want.
Good Luck
John


John
Re: First final inspection. #23432
03/21/03 08:55 PM
03/21/03 08:55 PM
C
CRW  Offline
Member
Joined: Feb 2001
Posts: 159
Bethlehem, PA USA
Hotline--you require CO2 detectors? My whole house is full of CO2! What should I do?

Re: First final inspection. #23433
03/21/03 09:57 PM
03/21/03 09:57 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
The CO2 detectors are to prevent global warming.

[Linked Image]

(My deepest apologies, John, I think I have called them CO2 detectors myself!!!)


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: First final inspection. #23434
03/21/03 10:29 PM
03/21/03 10:29 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Gentlemen:
My apology: Carbon Monoxide Detectors, not CARBON DIOXIDE. Guess that's why I'm not a senior chemest in some lab, white coat & all that.

John
PS: It's nice to know that someone reads the posts.


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,592 Are you busy
180,388 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 1.0097 MB (Peak: 1.1849 MB) Zlib enabled. Server Time: 2018-01-22 10:12:56 UTC