VFD'S #23163
03/12/03 09:04 PM
03/12/03 09:04 PM
S
sparky*62  Offline OP
Member
Joined: Jul 2002
Posts: 20
Ca.
I am having problems with a 2hp 460 volt vfd . It has blown the capacitors inside the drive. I megged the motor and wires and no faults there. It has happened twice. Any ideas?

Work Gear for Electricians and the Trades
Re: VFD'S #23164
03/12/03 10:14 PM
03/12/03 10:14 PM
W
WebSparky  Offline
Member
Joined: Feb 2003
Posts: 138
Cleveland, Ohio
vfd=variable frequency drive?

If so, make sure the incoming voltage is within range and not too low, especially if the drive is reversing during it's normal run cycle.

Just a hunch......

Dave


Dave
Re: VFD'S #23165
03/12/03 10:56 PM
03/12/03 10:56 PM
B
bigrockk  Offline
Member
Joined: Jan 2003
Posts: 174
Middle of Canada

Re: VFD'S #23166
03/12/03 11:39 PM
03/12/03 11:39 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
High temperature and overvoltage can be tough on electrolytic capacitors. Check line-side diodes to be sure one didn't fail, injecting AC into the DC bus/capacitor(s). Sometimes smaller VFDs become such a narrow-profit commodity that it’s cheaper to do a wholesale replacement. Some make good boat anchors—many do not.

Re: VFD'S #23167
03/13/03 12:42 AM
03/13/03 12:42 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
62,
What sort of cabling are you using between the drive and the motor?.
Is there any Mains-borne interference on the wires feeding the VFD, these units need a perfect Sine Wave input or there will be problems.
Unfortunately, you will need an oscilloscope,
to see what the waveshape is like, any harmonic interference on the lineside of the VFD, cause wierd currents to flow where they shouldn't.
Hope this helps. [Linked Image]

Re: VFD'S #23168
03/13/03 05:50 AM
03/13/03 05:50 AM
Z
zapped208  Offline
Member
Joined: Feb 2003
Posts: 197
Somewhere in USA
62,- This could be almost anything, like maybe a scr, rectifier, diode, or trim pot. Did you take it apart to see any possible over heating on the boards? Might be a good idea to call the drive's tech dept. for some help. did you disconnect motor leads from the drive before you meggered??


Shoot first, apologize later.....maybe
Re: VFD'S #23169
03/13/03 07:02 AM
03/13/03 07:02 AM
G
gramps  Offline
Member
Joined: Aug 2002
Posts: 112
ohio
check the output at the d.c. bus. should be between 700 and 800 VDC, for a 460 volt drive. if its not in this range, you prolly have an SCR problem.


gramps

Re: VFD'S #23170
03/13/03 11:01 AM
03/13/03 11:01 AM
P
Pearlfish  Offline
Member
Joined: Sep 2002
Posts: 83
Chicago Ridge, Il, USA
How much torque is on your load and what is your Decel time? If your decel time is too short you will have too much regenerative current feeding back into your drive. A properly sized braking resister might help.
JMHO

Re: VFD'S #23171
03/13/03 05:21 PM
03/13/03 05:21 PM
F
Format_C:  Offline
Member
Joined: Aug 2002
Posts: 29
Bridgeport, Connecticut, USA
What are VFDS? I thought it meant Vacuum Flourscent Display (VFD) Like the displays in VCRs, DVDs, Receivers etc. Those displays are also used in computers now.

Re: VFD'S #23172
03/13/03 05:27 PM
03/13/03 05:27 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Variable Frequency Drives

They control frequency and voltage supplied to standard AC motors so you can ramp them from 0 RPM to above the nameplate RPM if the motor can take it.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 12
Popular Topics(Views)
243,606 Are you busy
180,418 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.004s) Memory: 1.0224 MB (Peak: 1.2002 MB) Zlib enabled. Server Time: 2018-01-24 05:54:49 UTC