#217514 - 08/21/16 07:15 PM bonding two 200 amp main breaker panels  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
commercal service bonding two 200 amp services from a 400 amp meter with two sets of 3/0 cu to each panel no bonding allowed in meter can, do I tie both net together with a 1/0 cu from water pipe and a # 6 from ground rod and a #4 to each panel in the wireway and bond there or one #4 from the water pipe and one #6 from the rod to each panel.

Last edited by lite bulb; 08/21/16 07:17 PM.

2017 / 2014 NEC & Related Books and Study Guides

#217516 - 08/22/16 01:14 AM Re: bonding two 200 amp main breaker panels [Re: lite bulb]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
The easiest way would be to loop a GEC, based on the conductors feeding the panels (250.66) down from one to the water pipe, through the clamp and up to the other.
You can size to each panel. The other option is to run a GEC sized to the SE conductors (250.66) up towards the panels and splice the appropriate GEC from the panel to that.

From the handbook
[Linked Image]


Greg Fretwell

#217518 - 08/22/16 08:46 AM Re: bonding two 200 amp main breaker panels [Re: lite bulb]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I thought - and I'm begging for correction here- that:

A) No splices were allowed in the GEC; and,

B) You were never required (by NEC) to exceed #6 for the GEC.


#217520 - 08/22/16 04:57 PM Re: bonding two 200 amp main breaker panels [Re: lite bulb]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
You can't splice the GEC but you can splice a GEC "tap. Clear as mud huh?
That is why I said the easiest way is to loop one #4 or #2 through the pipe clamp and then you will not get a fight ... unless they actually want to size it to the SE conductors per 250.66

The GEC is limited to the rating of the electrode. A rod is #6, A Ufer #4 and a water pipe, the full size called for in 250.66


Greg Fretwell

#217521 - 08/23/16 08:56 AM Re: bonding two 200 amp main breaker panels [Re: gfretwell]  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
My question is can I tie the 3/0 net together in the wireway and do my bonding there dropping a #4 down to each panel


#217522 - 08/23/16 09:32 AM Re: bonding two 200 amp main breaker panels [Re: lite bulb]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,874
Brick, NJ USA
lite bulb:

"My question is can I tie the 3/0 net together in the wireway"

Do you mean to install 3/0 feeder into the wireway?? Or ??


John

#217523 - 08/23/16 09:55 AM Re: bonding two 200 amp main breaker panels [Re: lite bulb]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Great answer, Greg!

Another quibble I have with the artwork is that it appears to show a GEC that is larger than the service 'hot.'

Again, you're never required to have a BEC larger than the 'hot.'

I'm not sure you're required to have the GEC 'land' in every panel (or disconnect). As I see it, 1 meter = 1 GEC, land it in whichever panel is convenient.

No? I'm thinking of the meter bank at the apartment building across the street .... 12 meters, one GEC landing in one place.

Using Holt's explanation (ground rod for lightning / static only), I see the issue also as one grounding electrode for
each building. I don't see the pictured 'tap' as accomplishing anything at all.

XXXXXXXXXXXXXXXXX

As for lite bulb's second question ....

TWO sets of 3/0? A parallel feed? Well, that's a different way to do it ....

First, I'm uncomfortable feeding the panels without having a disconnect first.

I'd run 500's to a trough above the panels (as in the drawing), and tap off then with 3/0's for each panel (using NSI's).

Could you run your GEC taps up into that trough, splice them together and run the GEC from the trough to your electrodes? I don't see why not- assuming the trough remains accessible (not sealed by the PoCo).


#217524 - 08/23/16 01:36 PM Re: bonding two 200 amp main breaker panels [Re: lite bulb]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
The easiest way is to land the full sized 250.66 GEC in the meter/CT can and be done with it. Some PoCos may not allow that but it is the preferred method here.
You use an RNC nipple to get through the wall to the service disconnect with 3 (or 4 for 3p) wires and hit the bus with the MBJ. That satisfies the inspectors who don't want a parallel neutral path although, on the line side of the MBJ, I am not sure that matters.

A agree as soon as NFPA allows "taps" the idea of an unspliced GEC flies out the window.


Greg Fretwell

#217528 - 08/23/16 11:54 PM Re: bonding two 200 amp main breaker panels [Re: gfretwell]  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
Whats the differance between this and residental when you run two 200amp service cables out of a meter one to each panel?


#217529 - 08/24/16 12:29 AM Re: bonding two 200 amp main breaker panels [Re: lite bulb]  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
power co. will not allow bonding in meter box and the water pipe is to far away 200' to loop the EGC to each panel just thought it would be faster cheaper to do it this way.


Page 1 of 2 1 2

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.019s Queries: 16 (0.003s) Memory: 0.8203 MB (Peak: 1.0024 MB) Zlib enabled. Server Time: 2017-11-23 05:20:17 UTC