ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
Windows 7 update problem
by ampherder. 06/21/17 07:01 AM
Norwegian power?
by dsk. 06/19/17 03:40 PM
Anyone ever take a Furnas A14D drum sw apart?
by gfretwell. 06/17/17 08:14 PM
Mains supply in GDR
by dsk. 06/15/17 04:02 PM
Any UL 508 experts out there?
by sparkyinak. 06/07/17 05:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
238,125 Are you busy
173,288 Re: Forum
166,179 Need opinion
Who's Online Now
0 registered members (), 64 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Gallery
Next Gallery
Print Thread
Rate This Thread
Page 1 of 2 1 2
Images In This Group
IMG_1237.JPG
What's behind the door???
by HotLine1 on 02/22/15 07:59 PM

Found doing a walk-thru on a complaint
Have to check this out further next week.

Comments
#215026 - 02/22/15 08:45 PM Re: What's behind the door??? [Re: HotLine1]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,830
Brick, NJ USA
OK, it's back to the sideways pics!!!


(Fixed - Admin)

Last edited by Admin; 01/24/17 09:00 PM.

Super Rod Cable Installation Tools

Super Rod Cable Rod System
Super Rod Cable Rod System -
Voted
Best Product of the Last 50 Years by members of NICEIC


#215027 - 02/22/15 09:51 PM Re: What's behind the door??? [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,083
Estero,Fl,usa
I haven't got to OMG yet. How was the 250 stuff?


Greg Fretwell

#215028 - 02/23/15 02:50 AM Re: What's behind the door??? [Re: HotLine1]  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
John,

Is this supplied by a 1 Phase 3 Wire System, or a 3 Phase 3 Wire Corner-Grounded System?

BTW, Notice that most of the Grounded Conductors for the Branch Circuits are Fused.
The only one that is not Fused is at the bottom of the Bus Kit.

Nevertheless, quite a find!!! thumbs clap

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#215029 - 02/23/15 10:48 AM Re: What's behind the door??? [Re: HotLine1]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,830
Brick, NJ USA
I have to look at this in more detail.
It looked like the neutrals are all fused, except the tap off of the top buss.

It's in an old school bldg. More to come.


John

#215030 - 02/23/15 11:26 AM Re: What's behind the door??? [Re: HotLine1]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
I seriously doubt that the 'neutral bus' is fused -- it's a corner grounded delta -- hence the fusing to the 'neutral' it's a grounded 'hot.'

I absolutely HATE to sling around the term 'neutral' in such schemes. While a corner grounded delta certainly has been pulled over to ground potential, it absolutely has circulating current pumping in and out of it -- at a tempo far beyond the residual imbalances typical of a center tapped residential service.

[ Unlike a center tapped Service drop, one dares not ever break the bonding to the ground while power is applied. What's bad for a center tapped ground is horrific for a lifted corner on a delta. ]

[ EUSERC hates this old time scheme so much that you'd need a Presidential Executive Order to have a new one hooked up. Emergency responders will always mistake the grounded corner -- from the layout of the panel -- to be that of a single phase, center-tapped scheme. Not good. ]

Off hand, it smells like a distribution panel for site lighting.

Which is exactly the kind of system that would run on and on for years without an upgrade/ overhaul.

I'd expect that the service was some ancient 240 delta.

That far back 480 was just not done for such facilities.


Last edited by Tesla; 02/23/15 11:33 AM.

#215036 - 02/24/15 05:43 AM Re: What's behind the door??? [Re: HotLine1]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Since EUSERC hates corner grounded delta Services, I've never run across a single one.

I'd be interested to hear if a voltage tick reads 'hot' around such grounded legs of the power flow.

Let us know.


Tesla

#215047 - 02/24/15 05:36 PM Re: What's behind the door??? [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,083
Estero,Fl,usa
I used to see corner delta on sewer lift pumps. As soon as I figured out what it was, I never saw anything unusual about it. It seems to have a certain elegance to it. A grounded conductor is a grounded conductor. It is simply an arbitrary decision at which point we ground the transformer secondary. I would be a lot more concerned with the center of a wye when you have reactive loads than a corner delta. It will only draw nominal circuit current. The main code/listing issue is that there is 240v to ground so the 2 pole breakers need to be "delta" rated.


Greg Fretwell

#215052 - 02/24/15 10:38 PM Re: What's behind the door??? [Re: HotLine1]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Does it look to anyone else that many of the fuses have been replaced over the years? The labels on the fuses look too clean to be original. Why have they been replaced?


#215068 - 02/25/15 01:31 PM Re: What's behind the door??? [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,083
Estero,Fl,usa
They look like they are FRNs so they may have been instant blow before and someone decided a delay fuse was a better option.


Greg Fretwell

Page 1 of 2 1 2

Member Spotlight
Lostazhell
Lostazhell