#210006 - 05/21/13 06:24 PM What do you think?  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
[Linked Image]

This was submitted on another BB asking if it should be reported to the PoCo.

I think we all agree this needs to be fixed but I don't think I have ever seen the drop hung on the surface of the roof. (one anchor broke)

I assume the PoCo will swing a triplex from the mast when they get there.


Greg Fretwell

Tools for Electricians:

#210007 - 05/21/13 09:21 PM Re: What do you think? [Re: gfretwell]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,824
Brick, NJ USA
Greg:
Is that the remains of the mast insulator on the tight upper wire?

It's hard to tell, but is that the neutral & other phase leg laying on the roof?



John

#210009 - 05/21/13 10:37 PM Re: What do you think? [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
I zoomed this picture and it looks like the service drop was L/N/L across the edge of the roof and the Line insulator closest to the peak broke.
The white wire looping up over the roof looks like it might be TV cable. There is what looks like a 4 way splitter next to the service raceway on the gable end.

I am wondering if this 3 pack of insulators was originally on the fascia and the siding guy moved it when they did the re-skin.
I am sure we have all seen siding guys do strange stuff.


Greg Fretwell

#210012 - 05/22/13 12:34 AM Re: What do you think? [Re: gfretwell]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
"Power theft" was my first thought, but ...

Two lines coming from one direction, and the third from another? There's something very wrong going on here. I doubt the connections to the PoCo wires were made by a linesman, even though it does look like crimp connections were made. I'll bet there was no permit on a service change.

By all means, drop a dime- to both city and PoCo. Better yet, e-mail them with this pic- I'll bet it gets their attention.


#210014 - 05/22/13 02:12 AM Re: What do you think? [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
[Linked Image]


Greg Fretwell

#210021 - 05/22/13 02:03 PM Re: What do you think? [Re: gfretwell]  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Originally Posted by gfretwell


This was submitted on another BB asking if it should be reported to the PoCo.

I think we all agree this needs to be fixed but I don't think I have ever seen the drop hung on the surface of the roof. (one anchor broke)

I assume the PoCo will swing a triplex from the mast when they get there.
I seem to recall seeing some sort of roof mounted point of attachment thingy, but don't remember where.

POCO answers may depend on where this is.

On Long Island the POCO would not allow point of attachment to a conduit less than 2-1/2" GRC.

They'd have an issue with current point of attachment that can't be reached from a ladder placed on the ground. (looks like a small addition was added there to the right of meter.

My guess is (here) they'd want the POA moved up higher on the roof, or attached to Fascia (if solid support is there) in front of Mast.

Bill

Last edited by Bill Addiss; 05/22/13 02:04 PM. Reason: spelling

#210023 - 05/22/13 03:07 PM Re: What do you think? [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
I think FPL will allow the drop to go on a 2" GRC if there is a tieback brace behind it. I am not really sure what size that mast is tho.


Greg Fretwell

#210025 - 05/22/13 03:55 PM Re: What do you think? [Re: gfretwell]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,824
Brick, NJ USA
Greg:
PSE&G minimum is 2" for a mast, unguyed max height of 2 feet above the point of penetration. 2-1/2" is 4', 3" is 7'

The disclaimer within their handbook (Exibit 4) is 'PSE&G assumes no responsibility for damage with this install.

Point of attachment must have 3/4" hole for drop, free conductor length of 24", and no other systems shall be attached to mast.



John

#210039 - 05/23/13 09:49 AM Re: What do you think? [Re: gfretwell]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Editorial comment:

In doing service changes, I find moving the point of attachment from insulators on the structure to the mast a common task. If you have a mast, that's where the wires ought to be attached. Period.

In Nevada, the PoCo supplied the bracket. Here in Arkansas, I get one at the supply house. Either way, the cost is built into the job.

Is it required? Well, that's what the artwork in the PoCo standards shows ... looks like a requirement to me!


#210046 - 05/23/13 07:35 PM Re: What do you think? [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
This is what FPL says

Quote
4. Anchorage for Overhead Service Drop Cable or Wires
The Customer shall provide a safe and adequate anchorage for FPL's overhead service drop
conductors at the agreed upon location and height.
FPL will furnish, and the Customer will install, a suitable attachment for the service drop. The
attachment device furnished will vary, to be compatible with the type of building construction (Fig.
IV-6a thru 6c).
FPL WILL NOT BE RESPONSIBLE FOR DAMAGE TO THE CUSTOMER'S BUILDING OR
WIRING RESULTING FROM FAILURE OF THIS ANCHORAGE.


You own the pipe, they give you the hanger they want and the cable grip.

They actually bolted on the hanger at my house but they could have made me do it I guess. FPL also gave me the meter base and enclosure but I had to pick it up at their office. On my wife's houses FPL brought them out and installed them when they did the TUG. The builder paid the FPL contractor to run the lateral too. It was cheaper that way. A drop would have been free from FPL.


Greg Fretwell

Page 1 of 2 1 2

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 16 (0.002s) Memory: 0.8225 MB (Peak: 1.0056 MB) Zlib enabled. Server Time: 2017-05-24 04:03:31 UTC