#209023 - 03/03/13 09:39 PM Furnace circuit load  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Last question: Is any other equipment allowed on a circuit used for central heating equipment? If so what?

These questions (four questions) I've posted today are assigned to me as a code panel member at our next IAEI seminar held in Michigan. I appreciate your inputs and code references and will be used as part of my research and consensus. Names will be withheld to protect the innocent. smile


George Little

2017 / 2014 NEC & Related Books and Study Guides

#209026 - 03/03/13 10:53 PM Re: Furnace circuit load [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
Slam dunk

Quote
422.12 Central Heating Equipment.
Central heating equipment other than fixed electric space-heating equipment shall be supplied by an individual branch circuit.
Exception No. 1: Auxiliary equipment, such as a pump, valve, humidifier, or electrostatic air cleaner directly associated with the heating equipment, shall be permitted to be connected to the same branch circuit.
Exception No. 2: Permanently connected air-conditioning equipment shall be permitted to be connected to the same branch circuit.


Greg Fretwell

#209031 - 03/04/13 10:20 AM Re: Furnace circuit load [Re: George Little]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
I have seen where some AHJ's require the smokes to be on the heating circuit. They claimed that the homeowner would not be able to turn off the circuit in case the smokes went into alarm. This also happened to be before there were AC/Dc smokes.


#209048 - 03/04/13 08:51 PM Re: Furnace circuit load [Re: George Little]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Greg nailed it. The one that I'd forgotten about was the "Permanently connected air-conditioning equipment" has anyone ever dealt with this? To me a window shaker w/cord would not be considered "permanently connected".


George Little

#209049 - 03/04/13 09:32 PM Re: Furnace circuit load [Re: George Little]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
You know .... I don't have the documentation in front of me ... but that code provision sounds a lot like my writing .... it might have come from one of my proposals.

There was a time when some folks, especially at certain other "inspection" forums, would get all huffy if they found a circuit with a selector switch supplying both the heat and the AC. Or, if they found a duplex receptacle supplying the furnace, or if the humidifier built onto the furnace was powered by the same circuit, etc.

The NEC 'dedicated' circuit requirement comes after decades of the requirement only being found in the Mechanical code.


#209051 - 03/04/13 10:10 PM Re: Furnace circuit load [Re: George Little]  
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
One inspector in the area would not allow any part of an receptacle at a furnace for pumps,etc. to be left un-used. His reasoning was that the homeowner could plug a refridgerator or similar appliance into the un-used part of the receptacle.


#209055 - 03/04/13 11:25 PM Re: Furnace circuit load [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
I read that to be a central air conditioning system that shares the air handler with the furnace. If they are interlocked, they can live on the same circuit and in that case the A/C is the big load and the furnace is the small load. (unless you have toaster wire heat strips, that passes for a furnace here).
If you put a mini-split that was not interlocked with the furnace, on that circuit, I would have a problem with it.


Greg Fretwell


Member Spotlight
Admin
Admin
NY, USA
Posts: 3,439
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.002s) Memory: 0.7862 MB (Peak: 0.9423 MB) Zlib enabled. Server Time: 2017-04-30 08:56:35 UTC