ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 04/29/17 10:26 AM
201 volt equipment?
by bigpapa. 04/29/17 12:15 AM
Schneider LC1D09
by jraef. 04/28/17 11:05 PM
Electrode boilers question
by annemarie1. 04/27/17 01:40 PM
Why cables look like they do
by LongRunner. 04/26/17 09:36 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,940 Are you busy
169,768 Re: Forum
162,977 Need opinion
Who's Online Now
2 registered members (Admin, Ruben Rocha), 78 guests, and 18 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#20679 - 01/18/03 10:17 PM Fuse failure  
Nevin  Offline
Member
Joined: May 2001
Posts: 30
Lititz PA 17543
Had a case this morning where I had a 50 amp FRS-R fuse in a GE 60amp disconnect fail. I was not around when it occured however by all indications it really "blew" [Linked Image]. The top was burned out of the fuse and the line conductors above it had the insulation charred. the Red arc sheild was melted and sagging. These fuses are on a air compressor motor and normal amp draw is 29amps free running and 31amps under full load. I replaced the burnt conductors and checked out everything else. There were no line to ground faults and the resistance on the motor windings all check out normal. I replaced the fuse and fired up the machine everything ran normal.
What are the chances of a fuse failing like that for no apparent reason except for being a defective fuse? This compressor with these fuses has been in service for 3-1/2 years with no problems.
This incident also just reinforced in my mind the importance of have all open knockouts plugged and using the appropriate enclosure for the enviroment (dust etc). With the fire that blown fuse must have created, It would have been an ideal source of fire had it not been contained inside a proper enclosure.


Work Gear for Electricians and the Trades

#20680 - 01/18/03 10:28 PM Re: Fuse failure  
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
Sounds like high reistance in the fuse clip or the wire terminal caused the overheating.

There isn't much that can "malfunction" in a fuse that has a sufficiently high interrupting rating.

Ed


#20681 - 01/19/03 01:45 AM Re: Fuse failure  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
It's a judgment call, but overheated fuse clips can lose spring tension or 'bite'.

The books say one shouldn't be able to easily rotate [by hand] the fuse barrel.


#20682 - 01/19/03 02:16 AM Re: Fuse failure  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
There is a product to help when the fuse clips have lost their spring. Look at the TRON Clip-Clamps near the bottom of this page.
Don


Don(resqcapt19)

#20683 - 01/19/03 07:05 AM Re: Fuse failure  
maintenanceguy  Offline
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
I've come across fuses that were broken in half a few times. I figured that they burst or broke when they blew. No damage just alittle cleanup.

I suspect your burned wires and melted arc shield didn't happen in this instantaneous flash but that these things were hot for a long time from loose lugs or corrosion. Thats what I've seen melt those plastic arc shields and the wire insulation. Sometimes those arc shields look like a dali painting

[img] http://members.bellatlantic.net/~cruzan/forums/dali-time-icon.jpg [/img]


#20684 - 01/19/03 10:12 PM Re: Fuse failure  
lighthouse  Offline
Member
Joined: Jan 2003
Posts: 134
philadelphia pa 19125
Nevin...actually these fuses are under size per code.your FRS-R fuses (time delay)are calculated at 175% with your full load current of 31 amps x 175% = 54.25 amps you can go up to the next size 60 amps fuses.the 50 are under size.and maybe a loose connection on the wiring or the clip did not help either.


#20685 - 01/20/03 06:17 PM Re: Fuse failure  
Pearlfish  Offline
Member
Joined: Sep 2002
Posts: 83
Chicago Ridge, Il, USA
Nevin, What voltage is your compressor running at? FRS-R's are rated for 250 Volts. If someone accidentally grabbed the wrong fuses out of the drawer, (I've seen it happen) and installed them into a 480 Volt circuit. The results from the insulation breakdown would be consistent with the damage you describe.


#20686 - 01/20/03 07:28 PM Re: Fuse failure  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Bussmann FRS-R fuses are 600V rated.
It is their 250V family that is FRN-R.


#20687 - 01/20/03 07:30 PM Re: Fuse failure  
lighthouse  Offline
Member
Joined: Jan 2003
Posts: 134
philadelphia pa 19125
Pearlfish...there is no way you can put 250 volt fuses in a 600 volt fused disconnect switch or 600 volts fuses in a 240 volt fused disconnect switch.(they just will not fit)base on the fuses(FRS-R fuse) info.they are used on 480 volts circuits.rating 600 volts.in this case a motor load.

if it was 240 fuses the number would have been FRN-R

[This message has been edited by lighthouse (edited 01-20-2003).]


#20688 - 01/20/03 08:44 PM Re: Fuse failure  
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Is the photo I see in the this post on the violations section? https://www.electrical-contractor.net/ubb/Forum4/HTML/000215.html
It sure looks like what your decribe.


Page 1 of 2 1 2

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.003s) Memory: 0.8175 MB (Peak: 0.9938 MB) Zlib enabled. Server Time: 2017-04-29 15:41:48 UTC