#203201 - 09/14/11 12:58 PM Generator OCPDs  
Helectric  Offline
Member
Joined: Jan 2005
Posts: 90
Brandon, SD
Need some help. I have a portable 7.5 KW generator on a trailer. It's used to supply power to a portable job trailer in strip mining operations. The on board panel is a replacement that consists of a 40 amp back fed main and some single pole 20s. It's been hacked up pretty good and I want to replace it.
I'm thinking of using a Midwest panel with a 30 amp back fed main. Branch breakers would be (1) 30 amp, 2 pole GFI (for job trailer)and (1) 20 amp, 1 pole GFI (for genset mounted receptacle).
This is a new one for me so any comments or suggestions would be welcome.


2017 / 2014 NEC & Related Books and Study Guides

#203207 - 09/14/11 02:58 PM Re: Generator OCPDs [Re: Helectric]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,826
Brick, NJ USA
Sounds like a plan IMHO, but I'm not 'up' on mining rules & regs.



John

#203220 - 09/15/11 01:07 AM Re: Generator OCPDs [Re: Helectric]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
I would think that a 40 A main with a two pole 30 A GFCI and two or four single pole 20 A GFCI would be a better choice.

With a 30 A main and a 30 A GFCI, when fully loading the GFCI, you are in a race between both of the 30 A breakers.

Having two or four single pole breakers allows you to use mutiple small loads without one breaker trip making everything stop.

How do you deal with grounds and neutrals? Is the centertap of the generator windings tied to the generator frame? Is the generator frame bonded to the trailer frame? Do you drive ground rods or drag chains?

What does MSA state about temporary portable power for strip mines?



Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 15 (0.002s) Memory: 0.7521 MB (Peak: 0.8745 MB) Zlib enabled. Server Time: 2017-05-25 04:57:28 UTC