ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/19/17 01:02 AM
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,405 Are you busy
177,370 Re: Forum
168,975 Need opinion
Who's Online Now
0 registered members (), 17 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#200885 - 04/25/11 03:36 PM Difference in AC and DC disconnects  
bwise121  Offline
Member
Joined: Sep 2003
Posts: 114
Sacramento, CA USA
I just put in my first DC disconnect and for the life of me I can't see what the physical difference is. Besides the fuses is there a difference? Is there such a thing as a non-fused disconnect?

Thanks,
Byron


Work Gear for Electricians and the Trades

#200886 - 04/25/11 03:56 PM Re: Difference in AC and DC disconnects [Re: bwise121]  
Vindiceptor  Offline
Member
Joined: Mar 2011
Posts: 98
San Diego
Is this a PV DC disconnect?

Some manufacturer's have different arc chutes and most will require the use of multiple poles being used to facilitate the breaking of the DC arc.

Square D and Siemens both have wiring diagrams, have not used a Cutler-Hammer Disconnect yet.

Yes, you can get them as non-fused.

Last edited by Vindiceptor; 04/25/11 03:58 PM.

#200887 - 04/25/11 04:47 PM Re: Difference in AC and DC disconnects [Re: bwise121]  
bwise121  Offline
Member
Joined: Sep 2003
Posts: 114
Sacramento, CA USA
Yes, it is a 30 amp disconnect for a PV system.


#200888 - 04/25/11 04:58 PM Re: Difference in AC and DC disconnects [Re: bwise121]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
You can usually put a big diode across a DC contact to put out the fire.


Greg Fretwell

#200889 - 04/25/11 08:50 PM Re: Difference in AC and DC disconnects [Re: bwise121]  
Vindiceptor  Offline
Member
Joined: Mar 2011
Posts: 98
San Diego
Originally Posted by bwise121
Yes, it is a 30 amp disconnect for a PV system.


2 or 3 pole and how did you route the circuit through the disconnect?

What's the Isc for the circuit? That would determine whether you can run the circuit through a single pole, 2 or three (when 2 is required and you have a fuse, some manufacturer's want the fuse in the center pole 'B phase').

You can NOT route a circuit through a single pole and maintain the UL listing of the switch, Square D used to imply that you could, but they have since reworded their documentation.

I'm only mentioning this because I've seen a LOT of botched/non-code compliant designs and installs using 30, 60, 100 and even 200 amp 600 VDC disconnects with 3 circuits going through them.

We have been using combiner boxes with integral DC disconnects since mid 2009 because of the confusion with AHJ's, unfortunately, most don't even know what they're looking at when they're inspecting them, but they are definitely getting better and more informed since the PV market blew wide open.


#200894 - 04/26/11 01:38 PM Re: Difference in AC and DC disconnects [Re: gfretwell]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
You can usually put a big diode across a DC contact to put out the fire.

How will that help if the load is not inductive? The diode shorts out the inductive kick from a collapsing magnetic field because the induced voltage is the opposite polarity. A diode or even a RC network across contacts won't do much if the DC load is not inductive.


#200895 - 04/26/11 01:57 PM Re: Difference in AC and DC disconnects [Re: bwise121]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
Non inductive loads break cleaner.


Greg Fretwell

#200897 - 04/26/11 05:37 PM Re: Difference in AC and DC disconnects [Re: bwise121]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
The DC from PV arrays is NOT an infinite bus.

It breaks MUCH cleaner for that reason.

There is only so much energy flowing into the PV cells.

So even shorted PV DC does not produce the astounding arcs expected.

Not that I'd recommend trying it.


Tesla


Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.7936 MB (Peak: 0.9584 MB) Zlib enabled. Server Time: 2017-10-20 08:53:07 UTC