#200571 - 04/07/11 11:45 PM PVC BETWEEN GALV PIPE  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
I'm wiring a 480v motor from the starter I'm going down into the concrete floor with galv pipe to protect from damage, afraid pvc will get broken above the slab, then change to 70'pvc run in the slab then back to galv when I exit the slab to the motor. Does the code allow pvc pipe between galv


2017 / 2014 NEC & Related Books and Study Guides

#200572 - 04/08/11 12:18 AM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
Just be sure you bond the exposed sections of galvanized and run a hard wire EGC.


Greg Fretwell

#200576 - 04/08/11 08:13 AM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
I under stand the bonding of the exposed galv. and a grounding conductor in the pvc but what is a hard wire, is it a solid wire.


#200577 - 04/08/11 08:49 AM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]  
ghost307  Offline
Member
Joined: May 2005
Posts: 902
Chicago Illinois USA
I think Greg is saying that since you can't use PVC conduit to serve as a ground return path (equipment grounding conductor), sometimes known to its dear and intinmate friends as a 'ground wire', you need to run a physical wire through the conduit run to serve that purpose.


Ghost307

#200578 - 04/08/11 08:56 AM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
Yup, sorry, that must be an old timey or a regional term. I was referring to an equipment grounding conductor. Actually if it is bigger than #10 it can't be solid.


Greg Fretwell

#200587 - 04/08/11 08:05 PM Re: PVC BETWEEN GALV PIPE [Re: gfretwell]  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
Thanks for the help guys.


#200652 - 04/12/11 05:44 PM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Excuse me, but liquid wire will just slump down into the PVC.

It's going to have to be solid wire.

I prefer stranded.


Tesla


Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.002s) Memory: 0.7840 MB (Peak: 0.9407 MB) Zlib enabled. Server Time: 2017-05-24 00:22:08 UTC