MC cable supported by ariel Cable . Amperage rate? #190283
11/10/09 12:07 PM
11/10/09 12:07 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
600 volt three conductor (310.20??), or 4160 three conductor(310.73??) either with messager.
Yoopersup

2017 / 2014 NEC & Related Books and Study Guides
Re: MC cable supported by ariel Cable . Amperage rate? [Re: Yoopersup] #190284
11/10/09 01:21 PM
11/10/09 01:21 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
If the 3 conductors are in a metal jacket I don't think any "free air" table applies (one opinion).


Greg Fretwell
Re: MC cable supported by ariel Cable . Amperage rate? [Re: gfretwell] #190285
11/10/09 01:47 PM
11/10/09 01:47 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
IMO: Not only do you use the 'standard' table (310.16), but you might even have to derate for heat (in the sun), as you wpould were they over a rooftop.

I believe the 2008 also would require this MC to be in a waterproof jacket as well.

Re: MC cable supported by ariel Cable . Amperage rate? [Re: gfretwell] #190286
11/10/09 01:51 PM
11/10/09 01:51 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
310.73 MV : In Isolated CONDUIT in air. So that one I;m pretty sure of.
310.18 LV : Not sure of?

Re: MC cable supported by ariel Cable . Amperage rate? [Re: Yoopersup] #190295
11/10/09 04:30 PM
11/10/09 04:30 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
For the 600V, I think you may need to use Table B.310.3 in Annex B, since it specifically mentions type MC cable in free air.
For over 2000V though, with three conductors, I believe you could use table 310.71, since IMO, the MC jacket is not actually a conduit or raceway as defined in Art.100.

Re: MC cable supported by ariel Cable . Amperage rate? [Re: KJay] #190297
11/10/09 05:54 PM
11/10/09 05:54 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
I probably should have said you may want to use Table B.310.3 in Annex B.

Re: MC cable supported by ariel Cable . Amperage rate? [Re: KJay] #190314
11/10/09 11:40 PM
11/10/09 11:40 PM
S
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,328
Alaska
Just carious, why are you stringing MC on a messager? Or am just interpting something wrong here?


"Live Awesome!" - Kevin Carosa
Re: MC cable supported by ariel Cable . Amperage rate? [Re: sparkyinak] #190324
11/11/09 01:17 PM
11/11/09 01:17 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
MC cable on Industrial sites is quite often put on poles to remote pumping stations ect. Both 600v & i;ve even see 15kv in MC on poles.
Yoopersup

Re: MC cable supported by ariel Cable . Amperage rate? [Re: Yoopersup] #190326
11/11/09 01:25 PM
11/11/09 01:25 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I have never seen it before either, which tends to explain my silly answer above, sorry for the confusion. wink


Greg Fretwell
Re: MC cable supported by ariel Cable . Amperage rate? [Re: gfretwell] #190330
11/11/09 03:58 PM
11/11/09 03:58 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
mc cable 330.10 (B)4.

Installed outside of buildings or structures or as aerial cable.
type mc cable installed outside of buildings or structures or as aerial cable shall comply with 225.10,396.10,& 396.12.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,917
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 20
Admin 20
Potseal 13
Popular Topics(Views)
243,537 Are you busy
180,340 Re: Forum
170,829 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 16 (0.003s) Memory: 1.0226 MB (Peak: 1.2048 MB) Zlib enabled. Server Time: 2018-01-18 15:59:23 UTC