#18970 - 12/17/02 08:23 AM ground rod enclosed in cement?  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 817
NC
What do you do to enclose the opening for the ground rod before the cement is poured??
2" pvc collar?? then have one 6ft. away for the other ground rod?? just wondering the different ways that are used? I tried to find it in the code where it requires it, but hadn't found it yet, but inspector said it was suppose to be done??? Thanks for the help.. Steve


Work Gear for Electricians and the Trades

#18971 - 12/17/02 08:47 AM Re: ground rod enclosed in cement?  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
i was under the assumption a concrete encased electrode did not need an accessible connection......


#18972 - 12/17/02 08:55 AM Re: ground rod enclosed in cement?  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 817
NC
Sparky, last time I did a house and they poured a cement pad at the back, I drove the ground rod and run ground wire, then they poured the cement. When the inspector came and did my final, he said he would pass it this time, but said it should be accessable?? I can't find in the code where he's talking about. I figured he knew something I didn't.????? Steve....


#18973 - 12/17/02 10:09 AM Re: ground rod enclosed in cement?  
Chris Rudolph  Offline
Member
Joined: May 2001
Posts: 160
Winter Park,Fl USA
All ya'll Sparks,
There was an earlier posting that went on for some time and I believe the subject was about the approved connector for the concrete encased ground rod/rebar and the bare ground wire and other driven ground rods.If you find it some of your question may be answered.
Chris


#18974 - 12/17/02 10:50 AM Re: ground rod enclosed in cement?  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The exception to 250.68(A) says buried or encased connections are not required to be accessible. UL says that all ground clamps that are marked as suitable for direct burial, are also suitable for use in concrete.
Don


Don(resqcapt19)

#18975 - 12/17/02 04:54 PM Re: ground rod enclosed in cement?  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
thank you Don


#18976 - 12/17/02 05:36 PM Re: ground rod enclosed in cement?  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 817
NC
Thanks guys, I talked to the inspector today, and I think he was just meaning he wanted to See the connection first, before it was covered up. In my case of putting conduit under a slab for a sub panel to a separate building, I still left a 2" pvc "collar" in the form so He can see it when I have to drive the ground rod on the actual wiring of the building. He commented on going ahead and running the ground wire, but that would kind of be in the way of the concrete men pouring concrete, and also possibly damage the ground wire in the process of construction [Linked Image] Thanks for the input [Linked Image]
Steve



Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.002s) Memory: 0.7819 MB (Peak: 0.9343 MB) Zlib enabled. Server Time: 2017-04-24 19:09:44 UTC