ground rod enclosed in cement? #18970
12/17/02 07:23 AM
12/17/02 07:23 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
What do you do to enclose the opening for the ground rod before the cement is poured??
2" pvc collar?? then have one 6ft. away for the other ground rod?? just wondering the different ways that are used? I tried to find it in the code where it requires it, but hadn't found it yet, but inspector said it was suppose to be done??? Thanks for the help.. Steve

Work Gear for Electricians and the Trades
Re: ground rod enclosed in cement? #18971
12/17/02 07:47 AM
12/17/02 07:47 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
i was under the assumption a concrete encased electrode did not need an accessible connection......

Re: ground rod enclosed in cement? #18972
12/17/02 07:55 AM
12/17/02 07:55 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Sparky, last time I did a house and they poured a cement pad at the back, I drove the ground rod and run ground wire, then they poured the cement. When the inspector came and did my final, he said he would pass it this time, but said it should be accessable?? I can't find in the code where he's talking about. I figured he knew something I didn't.????? Steve....

Re: ground rod enclosed in cement? #18973
12/17/02 09:09 AM
12/17/02 09:09 AM
C
Chris Rudolph  Offline
Member
Joined: May 2001
Posts: 160
Winter Park,Fl USA
All ya'll Sparks,
There was an earlier posting that went on for some time and I believe the subject was about the approved connector for the concrete encased ground rod/rebar and the bare ground wire and other driven ground rods.If you find it some of your question may be answered.
Chris

Re: ground rod enclosed in cement? #18974
12/17/02 09:50 AM
12/17/02 09:50 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The exception to 250.68(A) says buried or encased connections are not required to be accessible. UL says that all ground clamps that are marked as suitable for direct burial, are also suitable for use in concrete.
Don


Don(resqcapt19)
Re: ground rod enclosed in cement? #18975
12/17/02 03:54 PM
12/17/02 03:54 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
thank you Don

Re: ground rod enclosed in cement? #18976
12/17/02 04:36 PM
12/17/02 04:36 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Thanks guys, I talked to the inspector today, and I think he was just meaning he wanted to See the connection first, before it was covered up. In my case of putting conduit under a slab for a sub panel to a separate building, I still left a 2" pvc "collar" in the form so He can see it when I have to drive the ground rod on the actual wiring of the building. He commented on going ahead and running the ground wire, but that would kind of be in the way of the concrete men pouring concrete, and also possibly damage the ground wire in the process of construction [Linked Image] Thanks for the input [Linked Image]
Steve


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,607 Are you busy
180,424 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9824 MB (Peak: 1.1360 MB) Zlib enabled. Server Time: 2018-01-24 09:22:52 UTC