wiring panel surge devices #18056
12/05/02 05:12 PM
12/05/02 05:12 PM
D
donles  Offline OP
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
When you wire a panel surge device, do you connect to the terminals of an existing two-pole breaker? Does the Code address this?
I got a call to check-out some electrical issues brought up by a home inspector. One issue was two wires to a breaker's terminals and I found the additional wires to be the two "hot" wires from the supressor. There is not room in the panel for a two-pole breaker dedicated to the supressor. Since the supressor is not a "load", I wouldn't think that it would matter if it's terminated on a breaker's load terminals along with the actual load, as long as it's a 15 amp breaker because the supressors wires look to be 14 AWG. . Hopefully, someone will say if it's a code issue.
A separate matter is that the breaker the supressor is connected to is the main breaker in a GE split bus-panel, so it's really the unprotected line terminals on the breaker. If someone chimes in and says it's OK to connect to a branch circuit breaker, I will move the wires to 2 15 amp breakers. If not, I will remove the supressor. In any event it's coming off of the main.
Don

Work Gear for Electricians and the Trades
Re: wiring panel surge devices #18057
12/05/02 05:30 PM
12/05/02 05:30 PM
E
Electric Eagle  Offline
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
Some breakers, such as Square D QO, are designed to accept 2 conductors of equal size. Most are not. I always give the TVSS its own breaker, most say to use a breaker 30 amp or less. Device wiring is allowed to be smaller than branch circuit wiring due to the short length. One option is to pigtail the TVSS with a 15,20,or 30 Double Pole, but make sure the device is rated for that breaker.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,863 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.004s) Memory: 0.9414 MB (Peak: 1.0580 MB) Zlib enabled. Server Time: 2018-01-23 00:03:45 UTC