Heated ice/snow melting mat #173352
01/08/08 06:37 AM
01/08/08 06:37 AM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Would a ice/snow melting mat require ground fault protection for equipment according to the NEC? According to the pdf below, it actually indicates no ground fault protection should be provided. I just wanted to make sure the instructions are not in conflict with the NEC.
http://www.barcoproducts.com/uploads/store_item_tabs/963B50AEF628490FA6BCCFF8CE85ACBE.pdf

Work Gear for Electricians and the Trades
Re: Heated ice/snow melting mat [Re: Frank Cinker] #173353
01/08/08 07:03 AM
01/08/08 07:03 AM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Frank,
Should be okay if the installation is in accordance with NEC 2008 210.8[A] and 210.8[B] exceptions.

Re: Heated ice/snow melting mat [Re: Frank Cinker] #173354
01/08/08 07:10 AM
01/08/08 07:10 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Quote
Note: Depending on the size of the mat being installed, a dedicated circuit without GFCI protection may be required. To disconnect the GFCI protected outlet, call a certified electrician.
At least they have built-in ELCI, right?

They may be referring simply to capacitive losses- a mat of this design is, by nature, going to shunt some current straight to ground by simple capacitance and may nuisance-trip the GFCI.

Every 15A or 20A outlet pretty much anywhere a consumer would be putting a cord-connected mat like this would have GFCI protection as absolutely required by NEC. The only exception would be an inaccessible dedicated outlet specifically for this mat, which is where the sparky comes in. Of course, they don't qualify this, and is joe homeowner REALLY going to pay to have a new dedicated outlet installed, or just defeat the GFCI he's got his extension cord plugged into when it starts tripping?

Last edited by SteveFehr; 01/08/08 07:15 AM.
Re: Heated ice/snow melting mat [Re: Frank Cinker] #173362
01/08/08 11:36 AM
01/08/08 11:36 AM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
I forgot to mention that the rating of the electric mat is 240 volts, 10 amps and is for a non-dwelling application.

Last edited by Frank Cinker; 01/08/08 11:38 AM.
Re: Heated ice/snow melting mat [Re: SteveFehr] #173363
01/08/08 11:38 AM
01/08/08 11:38 AM
S
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,328
Alaska
This is my read.

From the link:
Quote
Depending on the size of the mat that is being installed, a dedicated circuit without GFCI protection may be required.

Some of the mats are 240 volts due to their large size. The exterior GFCI requirement from 210.8(A) and (B) only applies to 125 volt, 15 and 20 amp circuits. Although it is not required for larger circuits, the property owner needs to decide the level of liability they are willing to take with the mat, especially if the mat is going to be in a public area. I presume these mats are tough but not bullet proof. With shoe cleats, high heals, and just general traffic will eventually damage it. Although it has ELCI protection, it is not the same as GFCI protection. ELCI has a higher tripping point. If a 240 volt mat were to be used, I would consider using a GFCI breaker especially if there is anything conductive within hands reach where the mat was going to be installed and the level of relaibility in that the mat will be properly inspected.


"Live Awesome!" - Kevin Carosa
Re: Heated ice/snow melting mat [Re: sparkyinak] #173442
01/09/08 09:30 PM
01/09/08 09:30 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
426.28 requires ground fault protection for the mat, however the built in ELCI provides this protection.
Don


Don(resqcapt19)
Re: Heated ice/snow melting mat [Re: resqcapt19] #173457
01/10/08 05:56 AM
01/10/08 05:56 AM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Thanks Don. That was the article I was looking for.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
Potseal 15
sparky 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,863 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 15 (0.007s) Memory: 0.9850 MB (Peak: 1.1387 MB) Zlib enabled. Server Time: 2018-01-22 22:09:24 UTC