#17256 - 11/22/02 03:01 PM How far is too far...  
nub  Offline
Junior Member
Joined: Nov 2002
Posts: 1
I am in the process of building a new house that sits about 600 feet off of the road. I would like to run power down the driveway (buried) for some lights and possibly an electric gate at the entrance.

Are there any special considerations to think about like voltage drop? If so, what would the recommended course of action be to achieve this goal?

Thanks in advance.


Work Gear for Electricians and the Trades

#17257 - 11/22/02 04:26 PM Re: How far is too far...  
RandyO  Offline
Member
Joined: Sep 2002
Posts: 30
Well, this is the way I would do it.

Putting the 6 switch disconnect rule aside,
I would run 10/3 on a two pole 30a breaker to a small breaker panel with only two 15a breakers I would have a means of disconnect at both sides.

If you need more than that it will start to get very expensive.

Use direct burial AND sch-80 PVC at 18" below ground.

But thats just me.

[This message has been edited by RandyO (edited 11-22-2002).]


#17258 - 11/22/02 05:21 PM Re: How far is too far...  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
#10 will have a 3% voltage drop at 2.5 amps, 120 volts on a 600' run.
Don


Don(resqcapt19)

#17259 - 11/22/02 05:53 PM Re: How far is too far...  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
lol!
[Linked Image]

.... what Don is politely alluding to is you need to do the math....i.e.-#of lights and wattage, gate motor's FLA for a load total, then size the branch, or fedder accordingly with VD considered..



Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7591 MB (Peak: 0.8905 MB) Zlib enabled. Server Time: 2017-04-27 22:39:35 UTC