How far is too far... #17256
11/22/02 02:01 PM
11/22/02 02:01 PM
N
nub  Offline OP
Junior Member
Joined: Nov 2002
Posts: 1
I am in the process of building a new house that sits about 600 feet off of the road. I would like to run power down the driveway (buried) for some lights and possibly an electric gate at the entrance.

Are there any special considerations to think about like voltage drop? If so, what would the recommended course of action be to achieve this goal?

Thanks in advance.

Work Gear for Electricians and the Trades
Re: How far is too far... #17257
11/22/02 03:26 PM
11/22/02 03:26 PM
R
RandyO  Offline
Member
Joined: Sep 2002
Posts: 30
Well, this is the way I would do it.

Putting the 6 switch disconnect rule aside,
I would run 10/3 on a two pole 30a breaker to a small breaker panel with only two 15a breakers I would have a means of disconnect at both sides.

If you need more than that it will start to get very expensive.

Use direct burial AND sch-80 PVC at 18" below ground.

But thats just me.

[This message has been edited by RandyO (edited 11-22-2002).]

Re: How far is too far... #17258
11/22/02 04:21 PM
11/22/02 04:21 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
#10 will have a 3% voltage drop at 2.5 amps, 120 volts on a 600' run.
Don


Don(resqcapt19)
Re: How far is too far... #17259
11/22/02 04:53 PM
11/22/02 04:53 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
lol!
[Linked Image]

.... what Don is politely alluding to is you need to do the math....i.e.-#of lights and wattage, gate motor's FLA for a load total, then size the branch, or fedder accordingly with VD considered..


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,589 Are you busy
180,383 Re: Forum
170,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.9575 MB (Peak: 1.0906 MB) Zlib enabled. Server Time: 2018-01-22 06:27:30 UTC