#169778 - 10/15/07 02:31 PM Large RV park Feeders Triplex underground  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 834
Michigan
Can 3 4/0 Alum. conductor triplex underground rated be in stalled in PVC conduit with a # 4 copper ground wire. If it meets 40 % fill single phase 120/240 volt. I'd say so want other views on this.?


2017 / 2014 NEC & Related Books and Study Guides

#169780 - 10/15/07 03:02 PM Re: Large RV park Feeders Triplex underground [Re: Yoopersup]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I don't see a problem Ernie as I understand your discription. I don't know of anything in the code that would prohibit using a copper equipment grounding conductor with an aluminum feeder. and I'm assuming that the triplex consist of all insulated conductors. See Ya in Troy in December.


George Little

#169781 - 10/15/07 03:56 PM Re: Large RV park Feeders Triplex underground [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,135
Estero,Fl,usa
Same question. Is the neutral insulated?


Greg Fretwell

#169838 - 10/17/07 06:53 PM Re: Large RV park Feeders Triplex underground [Re: Yoopersup]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 834
Michigan
Ground not a Problem , Neutrals insulated not a problem, I was curious about the Tri-Plex being in conduit underground?? Conductor fill for one thing I think would be different? Is tri-plex rated to be installed in conduit?? underground . I;ve also seen it done but wondered????


#169844 - 10/17/07 08:32 PM Re: Large RV park Feeders Triplex underground [Re: Yoopersup]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,135
Estero,Fl,usa
We did this a month ago. What is the insulation type ... USE? Other "wet" type?


Greg Fretwell

#169845 - 10/17/07 08:42 PM Re: Large RV park Feeders Triplex underground [Re: gfretwell]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 834
Michigan
What if its direct burial triplex??



Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.002s) Memory: 0.7758 MB (Peak: 0.9237 MB) Zlib enabled. Server Time: 2017-11-20 13:34:07 UTC