#167334 - 08/10/07 04:52 PM Comm bldg crawlspace sump pump GFI protected?  
frankgi  Offline
Member
Joined: Nov 2005
Posts: 11
NJ USA
It was recently brought to my attention, by an electrical inspector, that in a commercial building crawl space, a sump pump has to be GFI protected?? Instead of the usual dedicated single recept? I cannot seem to find anything that documents that...in 210-8 (B) anyway. Unless it really means "All"
Any thoughts?
FrankG
NJ


"Its all about the small details"

2017 / 2014 NEC & Related Books and Study Guides

#167336 - 08/10/07 04:59 PM Re: Comm bldg crawlspace sump pump GFI protected? [Re: frankgi]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,833
Brick, NJ USA
Based on reading '05 210.8 (b) I see NOTHING that pertains to the conditions that you describe.

That said, did you get a red sticker?
What Code Article was quoted?
You're in NJ, same rules apply statewide, unless there is a local adopted ordinance, which is highly unlikely.


John

#167339 - 08/10/07 05:45 PM Re: Comm bldg crawlspace sump pump GFI protected? [Re: HotLine1]  
frankgi  Offline
Member
Joined: Nov 2005
Posts: 11
NJ USA
Hi John,
No I did not get a red sticker. I was walking thru the inspection with him when he saw my single recept and made me aware of the required GFI. He did not quote an article, he even agreed that having a GFI nuisance trip will result in a flooded condition.(???)


"Its all about the small details"

#167347 - 08/10/07 07:14 PM Re: Comm bldg crawlspace sump pump GFI protected? [Re: frankgi]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,833
Brick, NJ USA
Frankgi:
OK, 'his' explanation and 'comment' are now noted. Could you PM me the area/location? Or my e-mail is in my profile.


John

#167361 - 08/10/07 08:20 PM Re: Comm bldg crawlspace sump pump GFI protected? [Re: frankgi]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I ran into that once. The inspector was a "combination inspector," and had been assured by the plumber (!!!!) that, of course, the pumps would be on a GFI. He was a bit surprised when I answered his question with a "Heck No!"

To give him credit, he did check with his boss, and did a 180 right then and there.

These 'seminar' inspectors are conditioned to think 'water + electricity = GFI" It takes a while for them to fully understand the topic.


#167372 - 08/10/07 11:02 PM Re: Comm bldg crawlspace sump pump GFI protected? [Re: renosteinke]  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
If this was a dwelling unit then the inspector would be correct as there are no exceptions to 210.8(A)(4), however there is nothing in 210.8(B) to require a commercial crawl space receptacle to have GFCI protection.
Don


Don(resqcapt19)


Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7775 MB (Peak: 0.9268 MB) Zlib enabled. Server Time: 2017-06-26 00:13:33 UTC