FEDERAL PACIFIC PANEL QUESTION #16380
11/11/02 01:09 AM
11/11/02 01:09 AM
W
wirewiz  Offline OP
Member
Joined: Jan 2002
Posts: 122
WA.
A new customer is opening a new sub shop. Existing Panel is an older FPE panelboard (one of the better ones I have seen) I still recommended they replace it. They are still thinking it over, Think I have them convinced!

Does anyone know of if the bolt-on type breakers are as bad as the stab-loc? Or, are they all garbage?


Thanks,
Wirewiz

[This message has been edited by wirewiz (edited 11-11-2002).]

Work Gear for Electricians and the Trades
Re: FEDERAL PACIFIC PANEL QUESTION #16381
11/11/02 07:21 AM
11/11/02 07:21 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I don't know if the problems associated with FPE apply to bolt-ons, but consider the availabilty & cost of new FPE bolt-ons. How much would it really add to his renovation costs to add a new panel?
Also, double-check the Short-Circuit rating of the old equipment. The utility may have upped the Xfmr at some point since the original pane was installed.

Re: FEDERAL PACIFIC PANEL QUESTION #16382
11/11/02 07:57 AM
11/11/02 07:57 AM
T
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
The biggest problem with FPE, IMHO, is that the breakers don't trip under fault conditions. The price, as Redsy pointed out, is "ungodly". I usually spare no effort in trying to get people to replace their old FPE equipment. If they won't pay me to do it though, I let them live it.

Good Luck,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
Re: FEDERAL PACIFIC PANEL QUESTION #16383
11/12/02 09:52 PM
11/12/02 09:52 PM
A
andylea  Offline
Member
Joined: Nov 2002
Posts: 29
ny
i just had a client pay 65 bucks for a federal pacific breaker. why did he buy it, cos his building super told him that that was what his problem was. the real reason, 220v ac line ran in conduit. wire was chaffed or damaged in the pipe, then there was a minor flood, and the federal pacific breaker must have put up one hell of a fight.eventually the wire did what the breaker was sposed to do.as a joke i asked the guy if he noticed any heat in the floor area around the ac unit. he actually replied that his wife had placed her clothes dryer horse there in that particular corner for years. i had to leave the appartment for a few minits........!


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,263
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,516 Are you busy
180,314 Re: Forum
170,811 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 14 (0.004s) Memory: 0.9580 MB (Peak: 1.0914 MB) Zlib enabled. Server Time: 2018-01-17 13:15:03 UTC