#15251 - 10/10/02 11:10 PM class 2 div 2 fittings  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
sealtight? waterproof? if i look in my truck boxes for a fitting, what do i look for? what qualifies in the class 2 div 2 zone?


Work Gear for Electricians and the Trades

#15252 - 10/10/02 11:40 PM Re: class 2 div 2 fittings  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Cindy,
Standard sealtight and fittings are fine for Class 2 Div 2. In Class 2 we aren't trying to contain an explosion like we are in Class 1, all we are trying to do is to keep the dust out of the electrical equipment and keep the electrical equipment surface temperature far below the ignition point of the dust involved.
Don


Don(resqcapt19)


Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.003s) Memory: 0.7426 MB (Peak: 0.8596 MB) Zlib enabled. Server Time: 2017-04-28 14:04:49 UTC