How do I do it Safely? #134914
12/06/02 10:10 PM
12/06/02 10:10 PM
electure  Offline
OP
Member
Joined: Dec 2000
Posts: 4,263
Fullerton, CA USA
I work with a couple of manufacturing companies that have home bases out of the US.
We've added 480x380,etc. transformers and odd buck/boost transformers (autotransformers) to spots as needed for the occasional odd voltage (here 277/480Y, 120/208Y are our nominal voltages).
I now have been "elected" to find a way to supply 100 volt power.
Does anyone have a source for this?
I only need about 30KVA, but I'm at a loss for the 100v 60Hz power, as the transformer doesn't seem to be available here in the US, and the manufacturer, in Japan, hasn't responded.
Thanks..S


[This message has been edited by electure (edited 12-07-2002).]

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: How do I do it Safely? #134915
12/07/02 12:36 AM
12/07/02 12:36 AM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Must the 100 volts be one 2-wire circuit? At 30kVA, that is 300 amperes. Safely designed maybe, but not cheaply.

Could the 100-volt load be split into 3 parts? That could reduce material costs some.

What is the acceptable voltage range for the nominal 100-volt equipment? Is a ~104-volt nominal acceptable?





[This message has been edited by Bjarney (edited 12-07-2002).]

Re: How do I do it Safely? #134916
12/11/02 07:22 PM
12/11/02 07:22 PM
electure  Offline
OP
Member
Joined: Dec 2000
Posts: 4,263
Fullerton, CA USA
Yes, Bjarney, a voltage of 104 is acceptable, and a 3Ø system would be fine!
The circuits will be be used for industrial process equipment. We're supposed to install a few of the branch circuits now, and the bulk of the capacity is to be used for future expansion. (I've not even seenany of the equipment.)

[This message has been edited by electure (edited 12-11-2002).]

Re: How do I do it Safely? #134917
12/12/02 01:17 AM
12/12/02 01:17 AM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
At http://www.federalpacific.com/literature/drytrans/FPTS-RTB-0701.pdf page 12, you could possibly use a 120:16V 5kVA {SB16N5F} transformer. that would buck 120V to 104V at 313 amperes. Else, if the “30kVA” feed was 4-wire wye, you could use three 2kVA {SB16N2F} transformers, each connected on a per-phase basis.

For 2-wire 120-to-104 volts connect 120V and 104V neutrals paralleled to H2/H4, with the 120V “hot” to H1/H3 and X1/X3, and 104V “hot” to X2/X4.

Use one 2kVA transformer for each 208Y/120V phase terminal.

Re: How do I do it Safely? #134918
12/20/02 10:07 PM
12/20/02 10:07 PM
electure  Offline
OP
Member
Joined: Dec 2000
Posts: 4,263
Fullerton, CA USA
Bjarney,
Thanks! I hadn't even thought about bucking this one down with autotransformers. Now they'll have their 104/180Y panel.
[Linked Image] Now what colors am I going to use for that one? (Only kidding, but heck I've about run out!)
Thx...S




[This message has been edited by electure (edited 12-20-2002).]

Re: How do I do it Safely? #134919
12/20/02 11:13 PM
12/20/02 11:13 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Been thinking about phase colors...how about puce, salmon and burnt sienna with a putty neutral?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 19
Potseal 13
Popular Topics(Views)
243,513 Are you busy
180,304 Re: Forum
170,802 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9761 MB (Peak: 1.1233 MB) Zlib enabled. Server Time: 2018-01-16 19:16:48 UTC