#129422 - 03/04/05 12:31 PM Article 250.4 (B)(2)  
unsaint32  Offline
Member
Joined: Aug 2004
Posts: 15
eden prairie, MN, USA
A quote from 250.4 (B)UNGROUNDED SYSTEM (2) , "[equipment bonding] shall be connected together and to the supply system grounded equipment."

Does the "supply system grounded equipment" indicate that the supply system is system-grounded? Or does that just mean that the suuply system's equipment bonding is connected to earth? (because an ungrounded system's equipment bonding gets connected to earth, but not to the power source)


Tools for Electricians:

#129423 - 03/18/05 03:35 PM Re: Article 250.4 (B)(2)  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
Means Equipment grounding(bonding) conductors well tie together to reference ground.An ungrounded system must be grounded the same as a grounded system even thought theres no reference from phase conductors to ground. Reason if one phase goes to ground(ground dector lights) nothing but an alarm or Ground dection light going out. BUT if one phase goes out then another the bonding conductors Must be able to carry fault.Why are theses systems used. Water treament plants, sewage plants areas where going dn at the ist fault is not a option. Gives the operator time when ist fault is noticed to schedule a shutdn and take care of the problem.Thats the way I see it. I;ve worked on several of theses systems as our power company well no longer supply a high leg delta but well supply an ungrounded or one leg grounded system.For better info see Electrical Grounding 6th edition (Ronald P.O;Riley page (90) or Soares grounding book



Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 216
Joined: March 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7435 MB (Peak: 0.8630 MB) Zlib enabled. Server Time: 2017-07-26 18:45:38 UTC