#127882 - 03/01/02 05:43 PM Foot Candles  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
I have a little booklet that lists recommended footcandle levels for certain locations. For a Warehouse it is 20-50 Fc. As an example, a 400 watt metal halide lamp has a lumen output of 25,000. My question is: how can I convert lumens to footcandles? Am I comparing apples to oranges? Any help would be appreciated.


Tools for Electricians:

#127883 - 03/01/02 07:04 PM Re: Foot Candles  
rmiell  Offline
Member
Joined: Nov 2000
Posts: 242
La Junta, Co. USA
I think the formula is as follows: 1(one) lumen falling on 1(one) square foot of space is equal to 1(one) footcandle. Or lumens/sq. ft. = fc

Since you did not give the area that you want to light up, change the formula around to read: lumens /required fc = sq ft covered. or 25000/20 = 1250 sq. ft. You can see that if you want a higher fc rating the area will decrease. 25000/50 = 500 sq. ft.

There are alot of other items to consider, initial lumens, dust, height, angel of the light to the surface, etc..

I believe Philips has some information on this, check their web site at www.lighting.philips.com/nam

Rick Miell


#127884 - 03/01/02 07:59 PM Re: Foot Candles  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Thanks for the information Rick. We have a "warehouse" application. 283ft. x 33ft. mounting height of 21ft. I'm considering installing (9) 400 watt metal halide high bay fixtures. That would give me 24 footcandles of light if my calculations are correct.

[This message has been edited by Frank Cinker (edited 03-01-2002).]


#127885 - 03/03/02 12:54 AM Re: Foot Candles  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Frank,

Try applying Photometric data to the desired Fc.

Foot-Candle Power would be the "Designing Level" [the light level that is desired] to shoot for.
The Lumens would be a figure of Light Output from a specific Luminare [Fixture and Lamp type].
Lumens per Watt would be the Efficiency Factors to consider when figuring the type of Luminare to be used.
Color Redention is another factor.

Apply these figures to Photometric Plots for various Luminares - in order to find a good design level of Fc.
The Photometrics will cover Fc at various levels.

Don't forget to include "Lumen Maintenence" factors with these calcs! This would include the Lumens available after lamps have been in service for a few Months.
These correction factors range from 20% to 40% reduction of output Lumens, as applied to certain lamps and fixtures. The Manufacturer[s] can supply this data, or you could figure a constant value yourself.

Rick has covered the basic calcs, along with other information very well!!

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#127886 - 03/03/02 12:31 PM Re: Foot Candles  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Scott,

Along with the information Rick provided I searched the internet and found the following web page. http://www.lightsearch.com/resources/lightguides/formulas.html


#127887 - 03/13/02 10:49 PM Re: Foot Candles  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Zonal cavity calulations take into account reflectances, installation heights, etc. See link below: http://www.hubbell-ltg.com/download/technicalpdf/Zonal_Cavity_Calc.pdf


Ron

#127888 - 03/15/02 09:54 PM Re: Foot Candles  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Frank,

I'll check out that link later today, then if time allows this weekend I'll post more to this thread.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!


Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7860 MB (Peak: 0.9412 MB) Zlib enabled. Server Time: 2017-09-25 06:14:18 UTC