ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Windows 10, who's upgraded?
by geoff in UK. 05/29/17 01:05 PM
How do you find a good employee?
by ElectricianBud. 05/27/17 10:58 AM
Recall notice: Bosch Solar panels
by ElectricianBud. 05/27/17 10:53 AM
Correct rotation, wrong sequence
by Potseal. 05/27/17 12:15 AM
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,983 Are you busy
172,001 Re: Forum
164,871 Need opinion
Who's Online Now
0 registered members (), 44 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#117384 - 06/06/04 10:34 PM Trailer-mounted Generator Violations  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,443
NY, USA
Quote
Here are some photos of a job site trailer-mounted generator. There are two loads, one is the wire in the PVC supplying the first job trailer and the second is the 10/3 extension cord supplying a second job trailer.

Based on these photos, can you spot the 6 code violations?

- Dave Nix
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]


Tools for Electricians:

#117385 - 06/19/04 03:37 AM Re: Trailer-mounted Generator Violations  
BigJohn  Offline
Member
Joined: Mar 2004
Posts: 391
Boston, MA
  • 1st Picture:
  • Conductors subject to damage - 300.4
  • No mechanical continuity of raceway - 300.12
  • Incomplete raceway - 300.18
  • Incomplete raceway and no support on raceway - 352.30
  • If that conduit is schedule 40 and subject to damage, violation of 352.12(C).
  • If one of the conductors on that lug is the GEC, violation of 250.64(B)
  • If that lug is not designed for use with that ring-connector, violation of 110.3(B).
  • 2nd Picture:
  • Aluminum GEC too close to the earth - 250.64(A)
  • Grounding electrode above grade - 250.53(G)
  • The connection of that GEC to the electrode looks really suspicious, possible violtation of 250.70.
3rd Picture:
Not sure. Maybe a violation of 400.8 or something in Article 552? [Linked Image]

4th Picture:
Taking a cue from the prominent "Schedule 40" and assuming the conduit is subject to damage - 352.12(C)

Anything I missed? [Linked Image]

Question: Since that generator isn't even required to have a grounding electrode, could it fail inspection because of the violations concerning the electrode and GEC? Could an inspector really say: "You don't need that electrode, but since you put it in, you gotta satisfy 250.56 by putting in another!" [Linked Image]

-John

[This message has been edited by BigJohn (edited 06-19-2004).]


#117386 - 06/19/04 09:29 PM Re: Trailer-mounted Generator Violations  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
I would guess that the job trailer, supplied by the extension cord in the third picture, would require a 120/240 volt supply and a 10-4 extension cord.



Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,138
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7539 MB (Peak: 0.8764 MB) Zlib enabled. Server Time: 2017-05-29 20:57:23 UTC