#105464 - 02/14/05 12:29 PM Wireway over stuffed with conductors!  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Quote
Joe,

Here is an interesting code violation that we found on a site visit for an apartment building remodel. Notice the wire way above the panels. It is so over stuffed with conductors that someone put in pieces of wood lathing to hold them in in order to get the cover on.
Mark Wilson
Electrical Designer


[Linked Image]

[This message has been edited by Joe Tedesco (edited 02-14-2005).]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#105465 - 02/14/05 04:15 PM Re: Wireway over stuffed with conductors!  
mamills  Offline
Member
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
Does it seem to anyone else that there are a tremendous number of wires/circuits coming home to this one small SqD panel? Considering the number of circuits 1) in the overstuffed wireway mentioned by Joe, 2) the romex/MC/etc. snaking down the wall surface, plus 3) the circuits moved over from what appears to be an old abandoned fuse panel in the wall, it seems that there would be several panels here.

Mike (mamills)


#105466 - 02/14/05 05:00 PM Re: Wireway over stuffed with conductors!  
markw  Offline
Junior Member
Joined: Feb 2005
Posts: 1
Mill Creek, WA, USA
The code violation in the picture is addressed in the NEC under 314.28, A, 2.
This would be a U-pull situation. The conductors are apartment unit panel feeders coming in from the meter center and out to the individual unit panels.


#105467 - 02/20/05 08:54 AM Re: Wireway over stuffed with conductors!  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
Lets see..... 9 conduits in...2 conduits out, HMMM!!!

Pierre


Pierre Belarge

#105468 - 02/20/05 02:31 PM Re: Wireway over stuffed with conductors!  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Encountered a similar situation not so long ago. In that case, the reason for the gutter was:
1) To split a circuit off to many different locations...several circuits fed outside lights along diverging paths;
2) To allow for the connection of timers to the circuits; and,
3) To make it easier to make changes....there really isn't much space on the top of the panel for multiple pipes.



Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 