0 members (), 1,001 guests, and 25 robots.
#99948 09/28/06 07:42 PM
We are debating, single vs. duplex right? Cause we all know it doesn't have to be GFCI'd
Most Inspectors we run into in michigan let it slide. Same goes for the duplex receptical at the disposal.
[This message has been edited by Trick440 (edited 09-28-2006).]
Shake n Bake
Workgear for Electricians
#99949 09/28/06 08:06 PM
Discussion....
GD on a dedicated circ? then single!
Micro (not on countertop) on dedi circ?, then single.
Decision/Opinion on the above from NJ DCA.
Two related HVAC devices on/at furnace, duplex; although some guys do two (2) singles in a 4x4.
#99950 09/28/06 11:43 PM
Since the code defines a max switch height at 6'7" to be considered readily accessible, I assume it to be reasonable to use this same height for receptacles. Thus it is not readily accessible, does not need to be GFCI protected, and cannot be used to comply with 210.52(G) 2002.
#99951 09/29/06 08:20 PM
Article 100 Definitions says "readily accessible" means you can reach it without the use of portable ladders...Iput me down for not readily accessible so no need for GFCI protection
#99952 09/29/06 08:29 PM
I could install the recept. without a ladder, I'd say it was accessable [Linked Image]