Member
Does the inspector allow a 120v. 15a. duplex receptacle to go non-GFCI protected if it is located on the 8 foot ceiling of an unfinished basement and the only thing plugged into it is a power vent for a water heater?


George Little
Work Gear for Electricians and the Trades

Workgear for Electricians

#99939 09/27/06 03:21 PM
Joined: Sep 2006
Posts: 58
Y
Member
Maybe, if it's changed to a single receptacle instead of duplex.

#99940 09/27/06 03:30 PM
Joined: Jul 2004
Posts: 10,056
Likes: 40
G
Member
How tall are the residents? Can they reach it without a ladder?

It all gets down to the definition of "readily accessible"
210.8(A)(5)ex1


Greg Fretwell
#99941 09/27/06 03:48 PM
Joined: Jun 2005
Posts: 821
S
Member
I agree with Yanici. Have them swap out the duplex receptacle for a single 120v/ 15a single receptacle. This way it is clear that the receptacles purpose is strictly for the power vent. A receptacle in an 8' ceiling is IMO not readily accessible.

[This message has been edited by ShockMe77 (edited 09-27-2006).]

#99942 09/27/06 11:05 PM
Joined: Jun 2003
Posts: 1,143
D
Member
+1 for the "dedicated" single receptacle.

#99943 09/28/06 01:11 AM
Joined: Jul 2004
Posts: 10,056
Likes: 40
G
Member
Intersting, Since the 8' ceiling is "readily accessible" to you guys, could this be the ONLY receptacle in the basement if it was GFCI?


Greg Fretwell
#99944 09/28/06 07:29 AM
Joined: Mar 2005
Posts: 1,213
S
Member
If this is the only receptacle in the basement, why not spend the $8 and put in a duplex GFCI so it can be used for general purpose? We can debate the letter of the law here, but we all know that dedicated simplex receptacle is going to sport a splitter and extension cord within a few months. Might as well look after the public safety here and err on the side of caution.

[This message has been edited by SteveFehr (edited 09-28-2006).]

Work Gear for Electricians and the Trades

Workgear for Electricians

#99945 09/28/06 05:54 PM
Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
Enforced here:
Sump, wtr htr, condensate pump,alarm, cent vac, etc.; in an unfinished basement area are single receptacles. Min. one (1) GFI duplex within each unfinished area(s).

John


John
#99946 09/28/06 07:07 PM
Joined: Jun 2005
Posts: 821
S
Member
John, would a duplex receptacle be acceptable in an unfinished basement if the receptacle served (2) condensate pumps serving the same furnace?

#99947 09/28/06 07:10 PM
Joined: Jun 2005
Posts: 821
S
Member
Nevermind.

210.8 (5) Exception No. 2