#99841 09/25/06 11:12 PM
G. Little- As far as I know he (the main spark) did not bond it. However, as I mentioned there was no power when the WH was installed so he might plan to bond it later. I'll have to ask him his plans sometime. Sorry I can't be more help right now.
#99842 09/26/06 02:32 AM
e57 Offline
You gents would have a hard time in my neighborhood. In general the whole area here will inspect for this: (Mandatory and no debate) Cold-water <5'of interior, Hot water at the heater no less than #8, and depending on the town or existing service either gas at the water-heater, or new services from the second fitting of the gas main to the main panel or electrode in less than #8. Hot-tubs and Jaccuzis bonded local to unit in #8+. The thinking is that any pipe in the building "may" become energized by any branch or even the service. And has been that way for a long-time here. It's a check-list item for them...
#99843 09/26/06 02:45 PM
Anyone else out there live in a jurisdiction that forbids (by the Poco) bonding of the gas line? I don't know the reasoning, but I know we never bond the gas line or meter. Can anyone explain this?
#99844 09/26/06 03:31 PM
Tripp- If you wire the furnace you bond the gas line automatically. The mechanical code will not allow a nonmetalic gas line.