1,141
9
Posts: 5,485 Likes: 5
Disconnect? We don't need no disconnect! At least, not for residential hot tubs.
The tubside "switches" I've seen are usually air-operated, with no electric anywhere near the water.
Posts: 10,056 Likes: 40
My neighbor has a hot tub that makes me shake my head. It is a real fancy thing with a LCD control panel and real switches right in the rim. It runs off a CMOS controller about 20' away via a ribbon cable. They have a U/L sticker on it but I don't know how you resolve that with 680. I asked the owner of the company about it and he blew me off like I was a moron. "That's low voltage, it doesn't count. Don't you know anything?". Since I really had no "J" in the game I had to just walk away shaking my head.
FWIW department- All equipment covered in article 680 with the exception of lighting is required to have a "disconnecting means" This disconnecting means must be within sight of it's equipment. (visible from it's equipment and not more than 50 feet away) I would not approve an air switch or a keypad as that disconnecting means no more than I would accept a stop/start station as a disconnect for a motor. As for the spa with the disconnect switch under the skirt of the spa where the motor/pump/etc is located I think it certainly qualifies as within 50 feet of it's quipment and visible. As for the 5' thingee in 680.22(C), I can say that the skirt with a removable panel provides the required barrier.
Hey! I can have my opinion.
For those inspectors that can't buy this - are you having the contractors remove this factory installed disconnect that's under the skirt of the spa??
This installation would not need an "Emergency Switch" if it were installed in a residential setting.
[This message has been edited by George Little (edited 09-27-2006).]
George Little
George, I agree with your fine point. The disconnect is a separate issue from the "emergency" switch. Please forgibe my sloppy thinking.
[This message has been edited by renosteinke (edited 09-27-2006).]
