Tom, we are now talking about apples and oranges. There are no requirements for the installation if it is hardwired but only where a receptacle is installed do you have requirements. IF a receptacle is installed, then the homeowner is likely to replace the equipment and rules are required. You are not required to install a receptacle so nothing has changed; however, if you install a receptacle, these are the rules. I fail to see the problem with this, you have a choice. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy

[This message has been edited by CharlieE (edited 10-29-2004).]


Charlie Eldridge, Indianapolis Utility Power Guy
Horizontal Ad
Joined: Aug 2003
Posts: 1,374
R
Moderator
I ws reading in the ROP, and the original proposal didn't include the requirement for an individual branch circuit. The proposal was simply to allow a cord and plug connection of a range hood, because from what I can tell under the 2002 it would be illegal. The CMP then added the five items that must also happen, such as the individual branch circuit. It was then voted on and passed 12-0.


Ryan Jackson,
Salt Lake City
Joined: Nov 2004
Posts: 7
J
Junior Member
In prior editions of the NEC, you are allowed to supply an exhaust hood by means of a cord and plug provided the appliance is intended or identified to be supplied in that manner. See 400.7(A)(8).

Joined: Nov 2004
Posts: 7
J
Junior Member
Section 422.16(B)(4) is under "FLEXIBLE CORDS". It is my opinion based on the ROP and ROC, that the individual branch circuit is required only when the receptacle outlet is intended to supply a cord-and-plug connected range hood. Where the range hood is hard wired, the requirements of 210.21 and 210.23(A) are applicable. An individual branch circuit is not required unless specified in the installation instructions for the range hood.

Joined: Jul 2004
Posts: 10,017
Likes: 37
G
Member
They keep adding required circuits and we may have to change the "42 pole" rule. They have bigger panels in the Canada market.


Greg Fretwell
Page 3 of 3 1 2 3

Link Copied to Clipboard
Advertisement:-Right
Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
Quirky 3
Popular Topics(Views)
369,175 Are you busy
291,480 Re: Forum
270,252 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5