ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left

Custom and Personalized Fall Gifts and Decor
Halloween Gifts and Decor

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 485 guests, and 7 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#97868 04/06/06 06:02 PM
Joined: Mar 2006
Posts: 7
T
Junior Member
While inspecting unit remodel in a multiple occupancy bldg I checked the bonding for the water piping system in the units panel. Traced the bond to the water heater of the unit. 250.104(A)(2) says in essence that if the system is isolated from all other occupancies by use of nonmetallic water piping then the above bonding is acceptable. The question arises: How do you know if there is nonmetallic isolation? You don't The building is old as the hills and who knows if the metal piping system has any isolated areas. So the real question is: If it is left bonded in the unit and there isn't any nonmeatlic isolation will it make a difference anyway? I hate to see the EC have to run a bond in an old building to the service.

Work Gear for Electricians and the Trades

Workgear for Electricians

#97869 04/06/06 08:23 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Is this a bonding conductor required by 250.104 or a grounding electrode conductor for the service?
Don


Don(resqcapt19)
#97870 04/07/06 06:15 AM
Joined: Mar 2006
Posts: 7
T
Junior Member
It's the bonding conductor per 250.104 for the water piping.

#97871 04/08/06 01:11 PM
Joined: Feb 2005
Posts: 693
L
Member
The older the building, the less likely there are isolated sections of pipe.


Larry Fine
Fine Electric Co.
fineelectricco.com

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5