#97478 02/21/06 10:52 AM
aldav53 Offline OP
When running multiple circuits from a panel to a juction box then splitting circuits off from there. I only need one ground to the junc box (sized to the largest conductor) then tie the rest of the grounds to a ground bar or lug from there. I don't need indivdual grounds for each circuit, unless its a GFI circuit. Correct?
Workgear for Electricians
#97479 02/21/06 12:17 PM
Are you talking about equipment grounding conductors? Then yes, you just need one, sized to the largest O/C device.
The GFCI question confused me.
#97480 02/21/06 01:24 PM
I don't know what a "ground" is. Are you asking about the grounded conductor or the equipment grounding conductor?
Don
#97481 02/21/06 03:14 PM
aldav53 Offline OP
Yes, equipment ground conductor. Not the neutral.
#97482 02/22/06 01:43 PM
Then I'd say your original question gets a yes answer but I don't see how the circuit being GFCI protected has any bearing on the question of the Equipment Grounding Conductor. Since the EGC does not pass through the sensing mechanism of the GFCI having only the one would have no effect on the GFCIs performance.
"This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison
[This message has been edited by tdhorne (edited 02-22-2006).]
Tom Horne
#97483 02/22/06 08:01 PM
aldav53 Offline OP
Your right, I probably don't need a separate ground for the GFI either, (neutral yes) but not ground. I'll just run the 3 - #8's for the spa heat pump to the pool equipment area junction box and branch off for the pool pump and GFI ground from there. I could run the motor frame bond wire there also. Where do they usually run the motor bond wire?
#97484 02/22/06 09:52 PM
The only place you need an insulated, unspliced EGC is to a pool underwater light J box.
#97485 02/24/06 01:25 AM
"then tie the rest of the grounds
to a "ground bar or lug"
how about some big blue wire nuts?
i have seen grounding conductors split bolted b-4, is it legal or smart for that matter to put several under a split bolt?
h20
#97486 02/24/06 07:53 AM
[quote}
h20
[/quote]
Nope. Split bolts are not listed for this use.