So guys, which one is it? Neutral counts as a current carrying conductor OR not? Which derating to use? 70% or 50%???
We dealing with a single phase 120/240V now.
Work Gear for Electricians and the Trades
Workgear for Electricians
#97136 01/26/06 01:27 AM
In single phase, the neutral only carries the unbalanced current. If you are seeing current on the neutral, the current on one of the phases is reduced that much.
#97137 01/26/06 01:32 AM
rknikko Offline OP
...and your answer to the question is....
#97138 01/26/06 01:52 AM
Don't count the neutral in the derating.