1 members (ampherder), 1,846 guests, and 8 robots.
#97108 01/23/06 06:17 AM
F
I'm tapping from the load side of the 100 Amp service disconnect and feeding a 20 amp overcurrent protective device located less than 10' away using 12 AWG wire in conduit. Is that Code compliant?
Workgear for Electricians
#97109 01/23/06 06:39 AM
Sounds good to me Frank.
George Little
#97110 01/23/06 10:54 AM
don't forget about the #12 in the split bolt....
Earl
#97111 01/23/06 10:30 PM
Is the OCPD going to be located at the top of the wood pole?
If yes, doesn't it have to be readily accesible?
...or no higher than 6'7".
[This message has been edited by ShockMe77 (edited 01-23-2006).]
#97112 01/24/06 09:29 AM
F
ShockMe77,
It will be located <=10' from the 100 amp service disconnect. (Click on the photo link I provided in my original post)
#97113 01/25/06 07:11 PM
Oh, I didn't realize the black outline was where the disco was going to be. I read the thread and thought the disco was going to be at the top of the pole. It didn't make much common sense to me.
#97114 01/25/06 09:06 PM
Frank
this sounds like it is compliant.... how are you going to tap the load side?
Pierre Belarge
#97115 01/26/06 06:17 AM
F
Split bolt connectors will be used. I'd like to tap 12 AWG to the 3 AWG. If a split bolt connector is not made to do so I'll have to use a larger guage wire as was suggested by the post by "earlydean" above.
[This message has been edited by Frank Cinker (edited 01-26-2006).]
#97116 01/26/06 01:36 PM
hey Frank, check out Ilsco.(www.ilsco.com)
they have lots of different "lay-in" type connectors for tapping, even for the sizes you are using. (never been a fan of split bolts) or like bossman said, try lug kits. just a suggestion.
http://ebusiness.ilsco.com/webapp/w...Id=-1&catalogId=1&categoryId=132
they even make covers for all their different taps/connectors.
(editted to add link)
[This message has been edited by goodwill (edited 01-26-2006).]
