The NEC has requirements for the jacket color (if covered) of equipment grounds. However, I can't find any such requirements for bond or grounding electrode conductors. What code reference would keep me from using a pink colored #6 Cu Thhn as a grounding electrode conductor to the water pipe (within 5' of its entrance to 100A serviced home) and then to bond around the water meter with a yellow wire of the same size?
BTW, I used #6 in my example instead of the minimum #8 since it can be run without any protection. I just wanted to state this so that there was no confusion.
[This message has been edited by triple (edited 12-07-2005).]
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Triple, there is nothing prohibiting this as far as the NEC is concerned.
Roger
|
|
|
|
Joined: Apr 2002
Posts: 197
OP
Member
|
Thank you Roger for your response.
I'd like to take this question one step further. Obviously I could not use white or gray in the above example since those colors are reserved for the grounded conductor. However, green wire (or black taped green) is often used for the grounding electrode conductor and/or bonding wires. Is this actually NEC compliant? Isn't green technically a color reserved for the equipment ground?
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
The code did not restrict the use of green for other purposes prior to the 2005 code. In the 2005 code the use of green is restricted to "grounding conductors". That will permits using green for GECs. Don
Don(resqcapt19)
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Triple: IMHO, 'green' or grn w/yellow stripe is the designated color for EGC, as well as bare.
As to using any of the above for the bond, I do not know of any NEC Article that would prevent it.
John
John
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
I have looked at lots of GECs, they called me the grounding inspector. Green tape over black THHN is the norm if it was insulated at all. That pretty much means it could be any color with green tape. I even think it could be white by the definition of "grounded conductor" Grounded Conductor. A system or circuit conductor that is intentionally grounded. but the confusion factor would have me asking for a penny's worth of green tape.
Greg Fretwell
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
I made a proposal to the 2005 Code that the GEC be identified in panels and switchboards to reduce confusion. It was rejected. Most electricians do this as a good work practice but, it is not required by the Code. On inspections I "recommend" that the GEC be identified, and usually it is but I can't require it. Alan--
Alan-- If it was easy, anyone could do it.
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
made a proposal to the 2005 Code that the GEC be identified in panels and switchboards to reduce confusion. It was rejected. As it shoukd have been. Who exactly was confused?
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
I have looked at lots of GECs, they called me the grounding inspector. Green tape over black THHN is the norm if it was insulated at all. I bet that's not all they called you. What is your basis for requiring this?
|
|
|