Just to clarify your thinking on 310.15(B)(6), should it happen to apply to other installations, service wires and feeders aren't the same thing. The definition of main power feeder has to be describing the last of the three conductor choices (feeders). There was no comma between "feeder conductors" and "that serve as the main...". If it was anything else, it wouldn't make any sense to have the service wires in the list.
There can be considerable debate as to where this feeder starts and end. However, I don't think anyone has ever questioned applying 310.15(B)(6) to service conductors (whether drops or laterals). It applies.