An alternative in many cases is to use reducing bushings with locknuts inside and outside.
An extreme gripe of mine is that small motors come with a 3/4" KO already knocked in them, heavily painted. It's a regular thing to find them with a 1/2" sealtite connector hanging by the conductors, RE washers floating around and a locknut floating on the inside :down:
What is with you guys? I'll bet that at least 1/2% of the times I've come across reducing washers, they have provided a good ground. I hate those things!
First off, reducing washers are heavily used in my side of the biz. (Cinemas) Mainly on the flex for the DC leads to the Xenon lamp, though. Seems that the manufacturers of that equipment can't get on the same page and design a standard KO size for a given lamp type.
And did any of you catch the doublespeak in this from the UL white book? (Bold emphasis is added by me.)
Quote
GROUNDING Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with ANSI/NFPA 70, ‘‘National Electrical Code.’’