1,186
15
My thoughts are as that the receptacle that is required 10'- 20' away really wouldn't pull that much power, (A radio and/or maybe a hedge clipper,etc.) Therefore, putting that outlet with the pump really couldn't hurt. However my real question is still, does it say that in the NEC that the pump motor has to be on a dedicated feed?
I have someone asking me this question, there is an AHJ that is requiring the filter to be on it's own dedicated circuit. There is no requirement from the manufacture that would fall under 110.3 (B), he already checked with the instructions.
Posts: 10,048 Likes: 38
I agree that you don't need a dedicated circuit but the 50% thing may make it a defacto thing if you have receptacles on the circuit. On the other hand they usually specify a gas heater will have it's igniter/valve circuit on the load side of the final pump disconnect to make sure the gas stops when the pump stops. That is going to be a fairly insignificant load tho.
I feel that MarkP gave the correct code reference. 210.23 -'02 NEC states that if there are fastened in place loads on the same circuit with lighting and cord connected utilization equipment, the fastened in place loads can't exceed 50% of the circuit rating. Reading on, any one single cord connected utilization equipment can't exceed 80% of the circuit rating. Most motors would no doubt require a separate circuit. I suppose if a pool pump were cord connected and there were provisions for quick disconnecting on the water (unions) it could be considered not fastened in place but that might be a stretch. My call would be a separate circuit ![[Linked Image]](https://www.electrical-contractor.net/ubb/frown.gif)
George Little
I'm running a dedicated circuit simply because it's common sense. Could you imagine, "honey, the television outlet isn't working, must be that pool filter acting up again." Of course you can't imagine that (even if you have come across something like this), because that does not make sense if you're a good electrician. The 50% load rule in 210.23 (A)(2) makes this very clear.
Posts: 7,413 Likes: 9
Harold:
We're talking AG pools right??
Twistlock; GFI, etc, etc??
OK, math time; step by step...
Continuous load..80%...20 amps....16 amp max. 50% = 8 amps or 960 watts; 1 HP = 746 watts, 1-1/4 HP MAX.
OK? take a 1-HP filter, using the math, NOT the nameplate.....
Resi panel, 3/4" PVC, #12 THHN/THWN; run to a GP GFI 10-20' from pool;continue to twistlock at pool filter, 5' from pool, w/bubble cover; 3' cord on filter; math acceptable!
I read 680 (2005) and don't see any prohibition for the above.
Give me a call, or an e-mail if you want; I'm curious??? I'll be at te PGA 'till 8/14, but the cell is on.
John, you are required to calculate the load for this motor using Table 430.248 which lists the full load current of a 1-hp motor as 16 amps at 115 volts.
Curt
Curt Swartz
Curt: You are 100% correct. I was using basic calcs to show that without using 430, a question that Harold referenced will arise.
This is a 'usual' discussion item at the counter, or on the phone to homeowners who want to be electricians. You went where I go, after they present their case for having the setup I outlined above.
Sometimes they already have it installed "their way" and have to re-do it.
The EC's get it right 98%.
John,
Yeah, it is an above ground pool and yeah, the math does work out. The thing is that most convinece receptacles don't use anything heavy around the A/G pool. IF you are going to install a lot of landscape lights etc., then by all means use dedicated circits and plan the whole job out. You don't need circuits tripping because we didn't do our homeowrk.
Harold:
Based on a 1/2 HP and larger, 120 volt, filter pump, a dedicated circuit IS mandatory, with either a GFI CB, or a 20 amp faceless GFI device mounted remote from the pool.
A 1/3 HP motor (7.2 amps) will work on a circuit 'shared' with another device(s); but, I can't remember seeing a 1/3HP filter.
As to the 'landscape lighting' that's a nightmare itself with a HO permit. Had one with 120 volt 'rope' lights installed around a IG pool; spliced and taped (red tape), on 2 extension cords, cause the "GF" outlet "kept shutting off" when I plugged the lights in.
John,
I didn't see this pool, I am just going by what a contractor told me. I think it is one of those small kiddie pools, You know the ones that are sort of easy to take down in the winter, not a full size A/G pool, and large enough to have a small filter. I will check back with him to see if it is a 1/3 hp or 1/2 hp motor.