ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 266 guests, and 9 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
#94249 07/21/05 07:36 PM
Joined: Jan 2004
Posts: 28
M
Member
OK I have a question for you guys…

We are currently roughing a house that uses all PEX tubing (plastic water piping.)

But, at every bathroom/sink/fixture, etc, they transition to copper in the walls.
So basically, we have several isolated copper water “systems” in the house supplied by this nonmetallic pipe.

How would you handle the bonding/grounding of this? I want to bond it all together, is that necessary?

Work Gear for Electricians and the Trades

Workgear for Electricians

#94250 07/21/05 07:59 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Code requires you to bond the metallic piping if it is likely to be energized. I might argue that a stand alone sink is not likely to become energized.


Ron
#94251 07/21/05 10:23 PM
Joined: Oct 2004
Posts: 135
B
Member
You could bond it to the circuit that it is likely to become energized by. If that makes sense. If it is likely to become energized at all.

#94252 07/22/05 10:02 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
This is not a pool area or hospital room. You do not have a metallic piping system, you have seperate pieces of metal.

If you are going to bond isolated sections of pipe simply because they are metal, don't forget to bond the towel and curtain rods. What about the couplings and connectors for the PE tubing?

If you are going to bond the piping because is near a counter top receptacle, then don't forget to bond the drawer pulls also.

Only if there is good probability that the metallic item will come in contact with an electrical conductor is bonding required. I can not think of a situation that would energize these pipe stubs.

#94253 07/22/05 10:41 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
I can think of a situation where the metallic pipe at the sink may be energized, point of use electric water heater, and if it were installed then I would verify that there was an EGC at the equipment to essentially bond the piping at the same time as the heater.


Ron
#94254 07/22/05 12:27 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
I agree 100% with JBD

Quote
You do not have a metallic piping system, you have separate pieces of metal.

No bonding required.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#94255 07/22/05 05:31 PM
Joined: Jan 2004
Posts: 28
M
Member
Thanks for the replies guys. I will leave it as it is.

Work Gear for Electricians and the Trades

Workgear for Electricians

#94256 07/22/05 07:41 PM
Joined: Jan 2002
Posts: 1,457
E
Member
Good to ask Matt but for some reason this question kills me everytime I hear it. Alot of people are quick to jump on the bond wagon [Linked Image] without actually thinking for a couple minutes about the situation.

#94257 07/22/05 08:23 PM
Joined: Jan 2004
Posts: 28
M
Member
Well, each bathroom has about 20 or so feet of copper in the walls, for shower, sink, etc.

Master is all copper so about 50 feet, but grounded by the steam shower unit.

NM can touch the pipe in some places.

How about the boiler? Allot of copper in the basement but PEX to the AH. So all that is grounded by the 14/2 to the boiler?

It all just seems a little unsafe. All because of plastic pipe.

#94258 07/22/05 08:52 PM
Joined: Dec 2004
Posts: 1,064
D
Member
This thread ponders the question:

How is any water pipe likely to become energized?

What is the criteria for likely?


Dnk.....

Page 1 of 4 1 2 3 4

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5