0 members (), 402 guests, and 8 robots.
#93676 06/06/05 06:07 PM
I agree. Bubble gum might even work! [Linked Image]
Ryan Jackson,
Salt Lake City
Work Gear for Electricians and the Trades
Workgear for Electricians
#93677 06/06/05 09:15 PM
I was fixin to ask what we thought an approved method was. I notice the cable company has a cool "serving" machine (for you sailors) that wraps a wire around the strand and the cable as it goes along. I am not sure what the wire is but it does seem to hold up in the sub tropics.
#93678 06/08/05 12:42 AM
How about messenger suppurted Liquidtight Metalic Cunduit?
Tom
#93679 06/08/05 08:24 AM
Nope. Don't even think about it. Only cables as listed in Table 396.10(A).Unless your in an Industrial setting then you can use a few other conductors.
George Little
#93680 06/08/05 10:06 AM
sides likidtite can only be 36" long max??
#93681 06/08/05 03:08 PM
Just joking.
Liguidtite flexable metal conduit has no NEC limit to length. As long as you have no more than 4 bends, it's not subject to damage, the operating tempiture is observed & supported per 351-8.
Not saying I would do unneeded piping with LFMC just that there is no NEC limit.
Tom