ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 326 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 4 1 2 3 4
#93294 05/15/05 06:28 AM
Joined: Jun 2004
Posts: 613
S
Member
gfretwell...

For the perpendicular intersecting #8 bonding wires of the equipotential grid pattern, I will use split bolt connectors...unless someone knows of a new product for this application?

I'm still in the design stage of rewiring this exsisting inground poured concrete swimming pool.

The deck surrounding the pool will be precast brick pavers set in stone dust... so the bonding grid under the deck would have to be placed under the layer of stone dust...

As for a grid under a fiberglass pool structure, here is the latest from the NFPA...

Go to: www.nfpa.org/itemDetail.asp?categoryID=136&itemID=19181 and click on "May 2005" from the list...

shortcircuit

Work Gear for Electricians and the Trades

Workgear for Electricians

#93295 05/15/05 12:29 PM
Joined: Feb 2002
Posts: 2,233
H
Member
George,

The Bonding Lugs I saw that looked AL, I believe were a type of metal that was "Tinned" to be UL acceptable for attaching to AL and they were suitable for direct burial. I will try to get more info on these lugs for you if interested. They are something brand new I guess, cause I never seen them before. I believe they were from Greeves.

#93296 05/16/05 11:34 AM
Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
Copper.org gave me 2 links to copper grid systems.
Erico (the Caddy Clip guys) makes a copper clad steel grid http://www.erico.com/products/GroundGrids.asp

Harger Lightning Protection makes a U/L listed #6cu grid http://www.harger.com/catalog2004/1_4_8.pdf

I don't know if either either of these is cheaper than a field built #8.
If the demand is there these would be the logical folks to cobble up #8 grids tho.


Greg Fretwell
#93297 05/16/05 06:46 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
For the perpendicular intersecting #8 bonding wires of the equipotential grid pattern, I will use split bolt connectors...
I don't think that is a listed use of split bolts.
Don


Don(resqcapt19)
#93298 05/16/05 08:15 PM
Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
Split bolt is a regular way to join 680.26 conductors. As long as it is listed for direct burial and copper I don't see an issue. It would be pretty expensive to do one on every corner of a 12" grid tho.
The Erico folks say they make it prewelded and ready to go. I looked at the catalog and didn't see a 3' wide mat. They seem to be 4'
If you are really buying some I imagine the salesman would be happy to talk to you.


Greg Fretwell
#93299 05/16/05 08:48 PM
Joined: Jun 2004
Posts: 613
S
Member
gfretwell...thanks so much for the supplier leads!

I put a call into HARGER and they gave me a part# for a mesh with #8 solid with welded joints 100ft long by 3ft wide...GM3100812

Coarse they won't sell directly, so I'll check with my supplier tomorrow for pricing.

I told him there is a demand for a suitable product in the pool industry.

shortcircuit

#93300 05/16/05 10:02 PM
Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
Actually I got those tips from copper.org but I was glad to help find an answer to this problem.


Greg Fretwell
Work Gear for Electricians and the Trades

Workgear for Electricians

#93301 05/17/05 06:06 AM
Joined: Jun 2004
Posts: 613
S
Member
resqcapt19.."Burndy Servit" split-bolt type KS-DB is UL approved for direct bury in earth or concrete...

shortcircuit

#93302 05/20/05 08:36 PM
Joined: Jun 2004
Posts: 613
S
Member
I ordered pre-fabricated grounding mesh from HARGER today. It is going to be 2 feet wide and 160 feet long, #8 solid copper welded at intersecting points with 12inch cells.

This will cost $620 for the mesh and $120 shipping and will take 7 to 10 days to get to me.

I was also successful busting into the concrete from the backside of the wall and exposed 1" rebar at two points for bonding the pool shell.

So, the 2005 code has added a couple grand to the electrical bonding for this pool [Linked Image]

shortcircuit

#93303 06/28/05 10:54 PM
Joined: Oct 2000
Posts: 3,672
Likes: 4
Administrator
Member
Quote
These are some pictures of an equipotential bonding grid installed around a swimming pool I installed today to satisfy 680.26

The installation took less than 2 hours, 1 man.

- shortcircuit
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Page 2 of 4 1 2 3 4

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5