1 members (Scott35), 537 guests, and 29 robots.
Hello,
Is the Service Load Calculated at 125% for a single family dwelling?
Can I use 65% of the nameplate rating for a heat pump system?
Thank you,
Brad
Tom Offline
1. No
2. No, but you might be able to use 65% of the supplemental electric heat.
Check out example D2(c) in Annex D for an example (2005 NEC)